[Equest-users] Baseline Pump Power
James Hansen
JHANSEN at ghtltd.com
Thu Jan 14 13:08:42 PST 2010
First you have to pull out the loop/pump flow from the PV-A report, then
multiply by 19 W, and enter that as the pump KW. I think you also have
to set the pump/motor efficiencies to 1.0 since the ASHRAE 90.1 value of
19 W / gpm should automatically include losses. Someone feel free to
correct me on that if it's not right.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Eckwahl, Tom
Sent: Thursday, January 14, 2010 3:59 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Pump Power
This question has been asked before but I could not find that a response
was posted to the forum. Baseline case hot water pump power is 19
W/gpm, where is this value input?
Thomas N. Eckwahl
Project Engineer, Mechanical
karpinski
ENGINEERING
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100114/d6f19264/attachment-0001.htm>
More information about the Equest-users
mailing list