[Equest-users] Lighting Control - Occupancy Sensor
Carol Gardner
cmg750 at gmail.com
Mon Jul 12 09:45:47 PDT 2010
Nick,
For occupancy sensors, I have always reduced the % on in the lighting
schedules, never the installed LPD. Here's a thread from way back discussing
how to do this:http://www.gard.com/ml/bldg-sim-archive/msg02168.html.
If the methodology has changed to reducing the LPD by 15% I'd like to know.
It would be much easier and I'd love to be wrong!
How are others doing this?
Carol
On Mon, Jul 12, 2010 at 7:42 AM, Nick Caton <ncaton at smithboucher.com> wrote:
> A small correction – the reduction (0-15%) is modifying the installed LPD
> (W/SF), not the schedules. The reduction amount does vary based on the
> table Carol referenced in 90.1 Appendix G.
>
>
>
> This is easiest to do in the wizards: there’s an overall multiplier,
> defaulted to 1.00, on the bottom of lighting load screen. In detailed it
> would require you to modify the space LPD values in the spreadsheet view,
> under the Internal Loads tab.
>
>
>
> Agreeing with Carol’s premise though – the way your question is worded
> suggests you weren’t clear on the contents Appendix G. For your own sake,
> definitely avoid relying on others to tell you what’s within 90.1 or you
> might find yourself in hot water down the road ;).
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> *Check out our new web-site @ *www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Carol Gardner
> *Sent:* Sunday, July 11, 2010 5:27 PM
> *To:* Derek Huang
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Lighting Control - Occupancy Sensor
>
>
>
> For the spaces that don't require occupancy sensors you can show savings by
> modifying the lighting schedule. I think a 15% reduction is allowed, but
> verify that by looking in Appendix G where it tells you what you can do and
> when. In fact it would be good for you to make a practice of researching the
> answers to these types of questions yourself and save the more complicated
> questions for the listserv. It is important to respect everyone's time and
> do diligence by trying to find the answers yourself. I know it's a lot to
> process at first but you will benefit from the study.
>
> Regards,
> Carol
>
> On Sat, Jul 10, 2010 at 6:21 PM, Derek Huang <Derek.Huang at atce.com> wrote:
>
> Does anyone know if there is a spot for Occupancy Sensor lighting controls
> ? In both of DD Wizard mode and Detailed Data Edit mode, I didn’t see any.
>
>
>
> Thanks,
>
>
>
> *Derek Huang, LEED AP, CPD *
>
> Mechanical Engineer
>
>
>
> *Error! Filename not specified.*
>
>
>
> 97 E. Brokaw Road, No 300
>
> San Jose, CA 95112
>
> *Direct*: 408 487-1305
>
> *Fax:* 408 436-1511
>
> www.atce.com
>
> derek.huang at atce.com
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
> Carol Gardner PE
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100712/1986d772/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100712/1986d772/attachment-0001.jpeg>
More information about the Equest-users
mailing list