[Equest-users] Sim Error
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Jul 1 11:16:42 PDT 2010
Omar,
Just guessing here. Using a chilled water system, you probably have a
coil curve called, "CHW-Coil-Cap-fEWB&EWT" as one of your Total Capacity
curves for one or more systems. Look for this in the "Cap Curves" tab
within the Cooling tab of the system(s). For some reason, your chilled
water loop is operating at 77F (EWT - entering water temperature) at
some point in the simulation, which is creating a negative value for the
coil curve. Perhaps your chilled water system is undersized.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Thursday, July 01, 2010 1:34 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Sim Error
Hi all,
I am running a simulation but it is not being completed. I am getting
this error in the .sim output file:
"Chilled water loop has a coil curve generating a negative capacity
ratio. Check the loop supply temperature, 77.F, for consistency with the
coil curves."
Can you please advise on this error; I really did not understand it!
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 255
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100701/93bdb563/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100701/93bdb563/attachment-0002.jpeg>
More information about the Equest-users
mailing list