[Equest-users] Corrupt Weather Files ??
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Jul 1 15:31:26 PDT 2010
John,
Try this:
In eQUEST, select Tools -> View File Locations -> View eQUEST Data
Directory to determine where your Weather folder is. Create a "TMY3"
folder within the Weather folder and put the TMY3 bin files (from
http://doe2.com/Download/Weather/TMY3/) in it. Go to Project Properties
and enter "TMY3\WEATHERFILENAME.bin" in the Weather File field, using
the appropriate weather file name.
Maybe the Tampa weather file got hit by lighting. I saw some gorgeous
T-storms when I lived/worked there.
Good luck,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Aulbach
Sent: Thursday, July 01, 2010 5:56 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Corrupt Weather Files ??
Has anyone used the Tampa Florida TMY2 weather file? I am getting
error mesaages trying to run with that weather. I try other weathers
with the same file, and they are successful.
BTW, how can I get the TMY3 BIN files to run, manually downloading them
and setting them up ??
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com <http://www.ptrenergy.com/>
<mailto:%7C%20jaulbach at ptrenergy.com> | jaulbach at ptrenergy.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100701/209e0327/attachment-0002.htm>
More information about the Equest-users
mailing list