[Equest-users] Please Help, Very URGENT- Hours unmet: 61.3%

Kosuke kosuke at cmtaegrs.com
Wed Jul 14 05:47:04 PDT 2010


Omar,
Your parking zone is served by heating only zone, but you still have cooling schedule. Your cooling schedule shows 99 degrees, but I can see that Beirut, Lebanon will be hotter than 99 degree. You need to take cooling schedule from all of parking zoning.

[cid:image001.png at 01CB2331.21F783B0]

Kosuke Kato, LEED AP
Senior Energy Modeling Engineer
CMTA Consulting Engineers, Inc.
Louisville KY - Lexington KY -Houston TX
Lou. 502 326 3085
Lex. 859 253 0892
Hou. 281 419 9899
kosuke at cmtaegrs.com<mailto:kosuke at cmtaegrs.com>
www.cmtaegrs.com<blocked::http://www.cmtaegrs.com/>
We've gone green! Please verify the necessity of printing this email - thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100714/d590ccdb/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 39898 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100714/d590ccdb/attachment-0002.png>


More information about the Equest-users mailing list