Hello Thomas,
I don't think you can make a construction where all the layers are R-value inputs. For a construction to have layers the program must be able to calculate some mass for the wall. If you want to specify only the thermal resistance of the wall choose "u-value input" when you create a new construction and put in the overall u-value for the wall assembly.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com<mailto:kvantassel at sustaineng.com>
[cid:image001.jpg at 01CB022F.9BFF2820]
We've moved. Please see below for my new contact info.
901 Deming Way, Ste. 201
Madison, WI 53717
608.836.4488 ext. 20| Fax: 608.836.4477
2009 Dane County Small Business Award Recipient
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Thomas Vu
Sent: Tuesday, June 01, 2010 7:38 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] BDL Error
All,
I get the following BDL error in my model
WALL has no heat capacity. U-Value used.
I am modeling the baseline envelope as prescribed in Appendix G of 90.1-2004.  Referring to Appendix A of 90.1-2004 to model the baseline envelope, I  created layers for the wall construction seen in the attached screenshot.  The resulting U-value for the wall is 0.124.  Can I not model a wall in this manner?  It seems specifying the U-value alone in the construction layer would do the same thing.
Thomas Vu, E.I.
Graduate Student
Dept. of Mechanical and Aerospace Engineering
University of Florida
vietdrum at ufl.edu
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100602/53d12407/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 31773 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100602/53d12407/attachment-0001.jpg>
    
    
More information about the Equest-users
mailing list