[Equest-users] Baseline Modeling
    John Aulbach 
    jra_sac at yahoo.com
       
    Fri Jun 11 11:28:06 PDT 2010
    
    
  
My two cents..
Before you make two Detailed Edit Models (one baseline, one proposed), make sure you have all the correct schedules and ancillary loads the same in ONE Detailed Edit model. You have quite rudimentary schedules in the Wizards (probably developed on Mars), so you need to insure any additional schedules (or schedule changes) and load additions are made.
THEN make your two Detailed Edit models.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
 
________________________________
From: Peter Hillermann <e190984026 at exchange.1and1.com>
To: Paul Buchheit <paul.buchheit at eesinet.com>; Omar Katanani <omar at ecoconsulting.net>; equest-users at lists.onebuilding.org
Sent: Fri, June 11, 2010 11:11:21 AM
Subject: Re: [Equest-users] Baseline Modeling
Thanks Paul,
 
Someone later told me I was incorrect and I’ll be changing the way I do it as well. Starting proposed and working backwards.
 
Thanks,
 
PETER HILLERMANN
 
peterh at westallarchitects.com
 
westall
architects
3404 pierce drive
 
o 770.458.4113
f  770.458.5352
c 678.898.2936
 
westallarchitects.com
 
 
 
From:Paul Buchheit [mailto:paul.buchheit at eesinet.com] 
Sent: Friday, June 11, 2010 1:23 PM
To: Peter Hillermann; 'Omar Katanani'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling
 
Hello Omar,
 
These are the steps I suggest you follow to complete the proposed building and the baseline building models most efficiently:
 
1) Model the proposed building first. Do everything you can in wizard. Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.
2) Save two new copies of your model- one for the proposed model to be completed in the detailed editor and one for the baseline model.
3) Complete the proposed model in detail editor
4) Go back to the model you saved in step 2 of this process as the baseline model and change your selections in the wizard to comply with ASHRAE 90.1. This is quicker and easier than changing all the values manually.Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.
5) Save a new copy of the baseline model and complete it in the detailed editor. 
 
This process allows you to do everything you can in the wizard for both the baseline and proposed building models. It also helps to ensure that schedules and other aspects shared by the two buildings are modeled the same as required by ASHRAE 90.1. 
 
 
I hope this helps,
 
Paul
 
 
 
 
Paul Buchheit 
Mechanical Engineer
EESI
phone: 541-754-1062
fax: 541-753-3948
paul.buchheit at eesinet.com
 
 
----- Original Message ----- 
>From:Peter Hillermann 
>To:'Omar Katanani' ; equest-users at lists.onebuilding.org 
>Sent:Friday, June 11, 2010 9:26 AM
>Subject:Re: [Equest-users] Baseline Modeling
> 
>Omar,
> 
>You need to start with the baseline then enter you efficient values. Yes you need to enter ASHRAE standards manually.
> 
>Thanks,
> 
>PETER HILLERMANN
> 
>peterh at westallarchitects.com
> 
>westall
>architects
>3404 pierce drive
>chamblee, georgia 30341
> 
>o 770.458.4113
>f  770.458.5352
>c 678.898.2936
> 
>westallarchitects.com
> 
> 
> 
>From:equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Katanani
>Sent: Friday, June 11, 2010 11:48 AM
>To: equest-users at lists.onebuilding.org
>Subject: [Equest-users] Baseline Modeling
> 
>Dear all,
> 
>I am modeling a school using eQUEST. I have entered the values corresponding to the proposed building (like the specifications given). I would like to model the baseline building according to ASHRAE 90.1 standard. 
>Do I have to change the U-values, HVAC strategy, Window/wall ratio, and the other stuff manually? That is, shall I open the ASHRAE standard and start changing all values one-by-one? The ASHRAE Standard 90.1 isn’t recognized by eQUEST such that it can create the baseline case alone? That would save a lot of time!
> 
>Best regards,
>Omar
>___________________________
>Omar Katanani
>Sustainable Design Engineer
>Email: omar at ecoconsulting.net
> 
>EcoConsulting (Lebanon)
>Chawkatly Building (Valli & Valli), 6th floor
>Charles Helou Street, Saifi District
>Beirut, Lebanon   
>Mobile:    +961 (0) 3 045 045
> 
>EcoConsulting (UK) Ltd
>28 Marshalsea Road
>London, SE1 1HF
>Tel:  +44 (0) 207 939 0989
>Fax:  +44 (0) 207 939 0981
>Website: www.ecoconsulting.net
> 
> 
> 
> 
> 
> 
> 
>
________________________________
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
chamblee, georgia 30341
      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/ede69e50/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/ede69e50/attachment-0003.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/ede69e50/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/ede69e50/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/ede69e50/attachment-0005.jpeg>
    
    
More information about the Equest-users
mailing list