Actually, provided you are eventually going into detailed mode, the
method you're showing (using "cutting walls") can produce fewer
adiabatic walls in the final result.
 
As an extension to this and a response to Otto's concern:  You will want
to delete the two face-to-face exterior walls that will be generated by
your footprint cut.  Doing so will not open the adjacent zones to the
world, but will make those sides have no heat transfer to/from anything.
 
If you build two shells, you will have two sets of "cutting walls,"
where the two shells join.  The wizards can automate making the joining
walls adiabatic, provided your footprint geometries are spot-on, but
ultimately you have two adiabatic breaks in your building with that
approach, whereas with this you have only one.  The other major
advantage is you are minimizing the number of shells with this approach
- very handy when you don't have to manipulate multiple schedules and
such later on.
 
~Nick
 
PS: it seems curious - based on what little I can tell - that you've
defined a custom "zoning pattern" that creates a perimeter zone on both
sides of your shell "cut."  This may be intentional, but I would
intuitively zone those areas to be tied to the core zone.
 
PPS: You may find much further discussion regarding this approach, if
you wish, by searching for the terms "courtyard" and/or "cutting walls"
in the archives.
 
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Wednesday, June 16, 2010 3:41 PM
To: Alex Krickx; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Modeling Courtyards
 
Alex, 
 
Break the shell into two shells. If you create one shell where the walls
are close but do not touch each other, you will have two exterior walls
where you do not want them. 
 
   
 
From: Alex Krickx [mailto:akrickx at seriousmaterials.com] 
Sent: Wednesday, June 16, 2010 3:24 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Courtyards
 
Hi all,
 
I'm hoping to get some advice on how to model a courtyard. I thought
I've seen some emails floating around about them, but couldn't find
anything in the archives. What's the best way to model a hole in a
building? Any help on this would be much appreciated.
 
 
 
Regards,
Alex Krickx
 
 
Alex Krickx
Building Energy Specialist
 
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
 
Warning: The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or
proprietary and confidential.  If the reader of this message is not the
intended recipient then you have received it in error and any review,
distribution or copying of this message is prohibited and you are to
notify us immediately by reply e-mail and delete the original message
immediately.
 
 
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity.   If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail.  Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful.   Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance. 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100616/6f70d7e1/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100616/6f70d7e1/attachment-0003.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 156 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100616/6f70d7e1/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 157 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100616/6f70d7e1/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 37517 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100616/6f70d7e1/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5602 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100616/6f70d7e1/attachment-0005.jpeg>
    
    
More information about the Equest-users
mailing list