[Equest-users] HVAC Schedules
    Omar Katanani 
    omar at ecoconsulting.net
       
    Tue Jun 29 06:46:10 PDT 2010
    
    
  
 
Ok so now I understand that the HVAC temperature schedules are actually
setpoints that are specified for each hour in the day. But shouldn't we
specify the setpoints from the thermal zone characteristics (design
heating temp and design cooling temp)? Will these two inputs override
each other?
 
Should I be using an ON/OFF schedule for the HVAC instead?
 
Please help as I'm really lost and out of time!
 
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
 
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel:          +961 (0) 1 971 255
Mobile:    +961 (0) 3 045 045
 
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel:  +44 (0) 207 939 0989
Fax:  +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/> 
 
 
 
 
 
 
-----Original Message-----
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com] 
Sent: 29 June 2010 16:01
To: Omar Katanani; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] HVAC Schedules
 
Omar,
 
When you start your project in the Wizard, HVAC schedules will be
generated automatically. Thermostat schedules will be created based on
the thermostat settings you enter on Wizard Screen 2 for the HVAC
system. The thermostat schedules that are created will be named
something like, "S1 Sys1 (VAVS) Cool Sch" and will appear in the Basic
Specifications, Cooling and Heating tabs for each of your HVAC zones
when you enter DD Edit mode. The thermostat schedules put your system
into cooling or heating mode based on the temperatures of your zones.
You will also have fan schedules (such as "S1 Sys1 (VAVS) Fan Sch") for
each HVAC system that control when the fans operate. A great way to
learn is to right click in each of the fields once you get into DD Edit
mode to access the help menu.
 
Regards,
Bill
 
 
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
  _____  
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Jackson, Alan
Sent: Tuesday, June 29, 2010 8:54 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] HVAC Schedules
 
Think of HVAC schedules as availability of the system to turn on, not
necessarily whether it actually is on or not. For instance a System can
modulate on its own even if the HVAC schedule is 1 (ON) for the whole
year.
 
 
Alan Jackson, LEED AP
KlingStubbins
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Tuesday, June 29, 2010 8:34 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HVAC Schedules
 
 
Dear all,
 
I honestly didn't understand the kinds of schedules for HVAC. My project
is a school. What are the options of the daily schedules of the HVAC
system? 
 
If the type is temperature, then what are these temperatures I have to
input every hour? Or shall I put it as ON/OFF and turn it on during
occupancy hours?
 
Any help is greatly appreciated!
 
Many thanks,
Omar
 
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
 
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel:          +961 (0) 1 971 255
Mobile:    +961 (0) 3 045 045
 
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel:  +44 (0) 207 939 0989
Fax:  +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/> 
 
 
 
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100629/e34329aa/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100629/e34329aa/attachment-0001.jpeg>
    
    
More information about the Equest-users
mailing list