[Equest-users] Control zone.
    Jackson, Alan 
    ajackson at klingstubbins.com
       
    Thu Jun 10 05:37:46 PDT 2010
    
    
  
Sambhav
 
When you have a multizone system where there isn't individual zone
control from either zone units or terminal devices there must be one
zone where the thermostat controls the operation of the multizone
system, typically this would be the case with a constant volume rooftop
unit for example. One zone has to ultimately control the system so that
zones aren't fighting each other to satisfy the setpoint. 
 
The number of unmet hours can be reduced by selecting a zone that
represents the load fluctuation of the other zones more closely.
 
Alan Jackson, LEED AP
KlingStubbins
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sambhav
tiwari
Sent: Thursday, June 10, 2010 5:32 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Control zone.
 
Hi All,
         What is the exact meaning of control zone ,and what is the
reason that by chaning the control zone our unmet hours gets reduced.
Please if any one can answer it i asked this dobut so many times but
could not get the reply.
Any response will be highly admirable.
Thanks
Sambhav.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100610/c6c35f59/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list