[Equest-users] Waterside Economizer
    David Bastow 
    dbastow at mcclure-engineering.com
       
    Mon Jun 28 11:29:55 PDT 2010
    
    
  
I have modeled water-side economizers successfully a number of times.  But instead of putting it under the chiller, as you are showing in your attachment, I have always input it on the air side.  To input the water-side economizer go under Air-Side HVAC and then under Cooling and then under Economizer.  After you are in this input area then the program will allow you to select that you want a water-side economizer and then when selected yes, will allow you to put in the water-side economizer inputs.  I have attached the helps that pull up in this area, when you right click and select item help.
 
David A. Bastow 
McClure Engineering, Inc.  
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Varkie C Thomas
Sent: Monday, June 28, 2010 11:08 AM
To: Varkie C Thomas
Cc: Sethi, Amarpreet; equest-users at lists.onebuilding.org; Jonathan Smith
Subject: Re: [Equest-users] Waterside Economizer
I am having a hard time getting �Chiller Type = Waterside Economizer� to work in eQ.  I received 2 messages recommending this as the solution.  I have 2 more saying that they have not been able to model WSE in eQ.  Please let me know if it is not supposed to work.  
 
Unlike DOE2.1E this is the only minimum input required in eQ.  In this project during WSE operation we require a Clg-Twr leaving temp (Plate & Frame HX entering temp) of 42F so that the CHW temp leaving the HX is 44F or 46F.  The eQ default is 85F.  Even with this default and �Chiller Type = Waterside Economizer� I get the error message �Condenser Water Loop has Zero Design Flow�.
 
Unlike DOE2.1E there is no way of attaching a schedule for WSE operation.  I have attached eQ input-output �Without-WSE-1� and �With-WSE-2�; DOE2.1E definitions of WSE commands and keywords;  a sample DOE2.1E plant section input showing WSE; a schematic of Plate & Frame HX; and my eQ input for WSE and the resulting error message.  The attached project is dummy to test eQ for WSE.
 
Has anyone modeled WSE with eQ?  WSE works with DOE2.1E commands and keywords.  Does Waterside Economizer work with EnergyPlus (this project is also going to be modeled with E+ using Design-Builder interface for building and systems), TRACE or HAP
 
Varkie
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100628/12ee94f9/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: water-side economizer.pdf
Type: application/octet-stream
Size: 153177 bytes
Desc: water-side economizer.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100628/12ee94f9/attachment-0002.obj>
    
    
More information about the Equest-users
mailing list