[Equest-users] eQuest - FCU with DOAS
Jonathan Curtin
jcurtin at WylieAssociates.com
Mon Mar 1 13:56:52 PST 2010
All,
I believe it is the RA temperature of the Dummy Zone that is passed to
the units with OA-From specified, so you are right John that the RA
would be too cold to return to an ERV, assuming your dummy space is
something around 55F.
I have spent many a late night trying to work around this problem and
can recommend the following approaches:
1. Model any Energy Recovery as an exceptional calculation (in a
separate model) for LEED
2. Incorporate the Energy Recovery into the FCUs or AHUs (although you
have to be really careful to properly account for your fan energy and
flow rates).
Regards,
Jonathan M. Curtin, EIT, LEED(r) AP
Mechanical Engineer
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Grando,
John
Sent: Monday, March 01, 2010 03:08 PM
To: James Hansen; Marcus Eliason; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest - FCU with DOAS
One further question that has been bothering me. How would you set up
ERV with the DOAS? I've seen some posts from the archives but none are
too clear. The return air temperature of the DOAS appears to be too low
to use an ERV on. Any suggestions?
John Grando LEED AP
-----Original Message-----
From: James Hansen [mailto:JHANSEN at ghtltd.com]
Sent: Monday, March 01, 2010 11:16 AM
To: Marcus Eliason; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest - FCU with DOAS
I haven't had a chance to look at your .inp file, but when you are
creating a DOAS system, make sure that you at least do the following:
1) Make sure the fan schedule is forced off at night and setback times.
2) Make sure the throttling range for the dummy zone thermostat is at
least 4 degrees (I usually use 6).
3) Make sure that the heating/cooling schedules that the dummy zone
follows are set to something like 120 degrees cooling and 20 degrees
heating after hours, just to make sure that a call for heating/cooling
doesn't show up in your report, and mess up the unmet load hours.
Just looked at your file: you need to specify some sort of minimum OA
control or minimum air schedule for the FCUs (I think). Right now
nothing shows up.
Also, why is the DOAS system serving so many "dummy" zones? I *think*
your DOAS system is EL1 Sys1 (SZRH), yet it is serving 20+ zones. I'm
confused...
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Marcus
Eliason
Sent: Monday, March 01, 2010 11:04 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest - FCU with DOAS
Hello,
I am trying to model a building with FCUs and a DOAS to deliver outdoor
air to the individual zones. I have put in the dummy zones for the DOAS
system, modeled as a single air handler with chilled and hot water
coils. I have changed the walls of the dummy zone to air walls,
specified the DOAS to get OA flow as sum of all zones and for the FCUs
to get OA from the DOAS. When I run the model, I get a lot of unmet
hours corresponding to the dummy zones and the DOAS system. I have
tried but cannot seem to turn off the return air path for the DOAS
(since it is 100% OA) and have specified the minimum OA fraction for the
DOAS as 1. I am not sure if the unmet hours means that my DOAS is not
adequately cooling the OA load or if it something else.
Also, my "pump & aux" energy in the model seems very high for a building
that only has 3 pumps. Can someone familiar with modeling DOAS shed any
light on what might be causing some of these problems. I have attached
the .inp and .pd2 files for reference.
Thanks,
Marcus Eliason
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com,
and destroy this communication and all copies thereof, including all
attachments. Thank you.
NOTICE OF CONFIDENTIALITY
This E-mail message and its attachments (if any) are intended solely for
the use of the addressees hereof. In addition, this message and the
attachments (if any) may contain information that is confidential,
privileged and exempt from disclosure under applicable law. If you are
not the intended recipient of this message, you are prohibited from
reading, disclosing, reproducing, distributing, disseminating or
otherwise using this transmission. Delivery of this message to any
person other than the intended recipient is not intended to waive any
right or privilege. If you have received this message in error, please
promptly notify the sender by reply E-mail and immediately delete this
message from your system.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
------------------------------------------------------------------------------
Legal Disclaimer: The information contained in this communication is confidential and is covered by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any of the information contained within this communication. If you have received this communication in error, please contact the sender by telephone at (713) 781-2526 or by response via email and permanently delete the original email (including attachments) and any copies.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100301/f1dfea7a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5651 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100301/f1dfea7a/attachment-0001.jpeg>
More information about the Equest-users
mailing list