[Equest-users] Fwd: no heating loads to systems --part II
    Pasha Korber-Gonzalez 
    pasha.pkconsulting at gmail.com
       
    Mon Mar  8 07:29:55 PST 2010
    
    
  
Thanks John/Vik- Yes. but when I do put in reheat that is the only way the
systems are receiving reheat, so my question is why are the heating coils
not doing the primary heating wherefore in my case file, all of the heating
is up to either reheat (specified by me) or via baseboards (also specified
by me.)
The big question is:  why aren't the heating coils doing the job first, and
then the excess is to be made up via reheat and/or baseboards.
I have not specified any input for humidty control (based on the help file
recommendations--b/c we don't have humidification control in the proposed
building...
The DOE2 help file indicates:
REHEAT-DELTA-T
Maximum increase in temperature for supply air passing through the zone (or
subzone) reheat coils. The value specified here applies to all zones in the
system. This keyword is required in order to simulate heating the air as it
passes through the terminal reheat coil. Note that when very little air is
passed (see MIN-FLOW-RATIO) there may be insufficient reheating.
The highlighted statement is noted, but it still doesn't indicate that this
input is required *in order to simulate any heating requirement.*  It only
states it is required to simulate reheat heating requirements.  Why don't
the heating coils work in my model is my "black & white" question....  all
in all my space heating energy (with reheat & baseboards) is only 1% of the
total building energy for a climate in Vancouver, BC...  why is it so low?
...if I am just really missing something---please don't hesitate to tell me
so. ---- I have also specified the hot deck temp coming off the htg coils
which then gave me some capacity in my heating coils, but unfortunately by
adding this input  all of my numbers have dropped instead of increased.
I also looked back into the archives to find an answer to this issue--I
found two others who were having the same problems I have, but they have
responded that they never figured out the problem either...
Pasha
On Sat, Mar 6, 2010 at 10:34 PM, John Aulbach <jra_sac at yahoo.com> wrote:
>  Pasha:
>
> I believe the short answer to this is that not all VAV zones have reheat.
> Therefore, you need to put reheat in the zones that have it. otherwise, all
> systems would get reheat.
>
> John Aulbach
>
>  ------------------------------
> *From:* Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com>
> *To:* eQUEST Users List <equest-users at lists.onebuilding.org>; Vikram Sami
> <vsami at lasarchitect.com>
> *Sent:* Sat, March 6, 2010 9:30:09 PM
> *Subject:* [Equest-users] Fwd: no heating loads to systems --part II
>
> Thank you both for looking at this.  I'm a bit dumbfounded that it can't be
> as easy as the fact that I need to specify reheat, since I have indicated
> that it is a VAV with reheat system, but if that is the case then I will
> re-instate the reheat delta t so that I can generate heating energy.   (when
> I had input a reheat delta t of 30 degrees F, I was able to successfully fun
> a simulation, but the heating energy numbers where so high (i.e. 30 kWH/sq
> ft or more) that it just didn't seem like this was the correct input for my
> model.
>
> I just think that it is a bit weird even for the programming that the only
> way I can get heat out of the heating coil is that I have to enlist reheat
> or baseboards in order for the system to assume that there is a heating
> load.
>
> I understand the logic of why this works, but I don't understand why it is
> a requirement in DOE to have some or ll of the heating capacity specified
> for it to "autosize" or react to the fact that heating loads need to be
> passed to the systems module only if reheat or baseboards are specified.
>
> If it is possible for any of the eQuest programmers to comment on this
> input requirement I would like to hear thier feedback.  In the meantime,
> what I am understanding is that it is a requirement to specify supplementary
> heating (i.e reheat or baseboards)  in DOE2 for a VAV reaheat system before
> DOE2 will allow a basic heating coil to assume a heating load...somebody
> please tell me I'm wrong-because this doesn't make sense.
>
> Pasha
>
> ---------- Forwarded message ----------
> From: Seun Odukomaiya <sodukomaiya at laceindy.com>
> Date: Sat, Mar 6, 2010 at 4:59 PM
> Subject: RE: [Equest-users] no heating loads to systems --part II
> To: Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com>
>
>
>  Pasha,
> I took a look at your model. When employing a VAV-Reheat System as you have
> in your model, you must also specify the reheat Delta-T for the zone heating
> coils attached to the units (see attached screenshot). If this is not done,
> the program assumes that the zones have no reheat, and thus will never put a
> load on your hot water loop. This, in turn, causes the error that you've
> seen. The DOE-2 documentation describes it as follows:
>
>
>
> Maximum increase in temperature for supply air passing through the zone (or
> subzone) reheat coils. The value specified here applies to all zones in the
> system. This keyword is required in order to simulate heating the air as it
> passes through the terminal reheat coil. Note that when very little air is
> passed (see MIN-FLOW-RATIO) there may be insufficient reheating.
>
>
>
> According to your model, the maximum zone entering supply air temperature
> is 105 degrees. I also noticed that your zone minimum entering supply
> temperature is 55 degrees. As such, you need to specify your reheat delta-T
> as 50 degrees (as in the screenshot). This ensures that your zone coils are
> able to raise the 55-degree air from the AHU up to the 105 degrees that you
> have specified. Try that, and your model should run just fine.
>
>
>
> *Seun Odukomaiya, LEED AP  -  **Mechanical Engineer*
>
> L'Acquis Consulting Engineers
>
> 9229 Delegates Row, Suite 550
>
> Indianapolis, Indiana 46240
>
> voice:  (317) 706-2075, ext. 255
>
> fax:     (317) 706-2076
>
> email:  sodukomaiya at laceindy.com
>
> web: www.laceindy.com
>
> P* **Please consider the environment before printing this e-mail.*
>
>  ------------------------------
> *From:* equest-users-bounces at lists.onebuilding.org [
> equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
> Korber-Gonzalez [pasha.pkconsulting at gmail.com]
> *Sent:* Saturday, March 06, 2010 4:26 PM
>
> *To:* eQUEST Users List
> *Subject:* [Equest-users] no heating loads to systems --part II
>
>    Hi all,
>
> okay-I'm back to where I was last time I posted this question:  why are
> there no heating loads being passed to my systems?
>
> Here's the story: (160,000 sf high school building)
>
> The attached file is my baseline 90.1 model using System 7 (VAV w/reheat)
> As the file is now-I have removed the reheat delt-T (30 deg), and removed
> any baseboard heating in all /systems/zones and removed any input of heating
> capacity of the coils.  With this, my file receives the following error:
>
> ***ERROR***********************************************************************
>
> Loop: Hot Water Loop has zero design flow.
>
> Check input for consistency, or specify design loads.
> Right now I am trying to have DOE2 'autosize' anything it can so that I can
> get a good run and go back and adjust equipment capacities....but I don't
> know where else I can look further for why the systems aren't receiving the
> design loads.---thus creating the above error.  Something is stopping DOE
> from passing the loads to the systems.  When I open my sim file, the only
> reports being produced are the L-reports.
>
> If anyone has any hints or can take a look to find what it is I'm
> missing--I know it's a simple thing, but can't seem to find why it is doing
> this.  (I've been staring at these files tooo long...)
>
> ---on a side note--after all the help I received with this issue earlier
> this week I have input all of the temp schedules that are required, and all
> that I know needs to be input to get the systems to run.  any help would be
> greatly appreciated so I don't have to go back and rebuild this model from
> the beginning....I'm too close to the end to go back and rebuild
> another file.
>
> Thanks in advance!
> Pasha
>
>
>
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/d91fc645/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Port Alberni March 7 ddedit baseline.pd2
Type: application/octet-stream
Size: 100234 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/d91fc645/attachment-0002.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Port Alberni March 7 ddedit baseline.inp
Type: application/octet-stream
Size: 253000 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/d91fc645/attachment-0003.obj>
    
    
More information about the Equest-users
mailing list