[Equest-users] External Wall Calculation
Grando, John
JGrando at cosentini.com
Wed Mar 17 13:09:50 PDT 2010
Scott,
Thanks for the explanation, at least now I know I shouldn't bother banging my head against the wall on this one. Does anyone have any tips for changing infiltration CFM/SF of exterior wall without going through each zone and manually calculating it?
John Grando LEED AP| Mechanical Engineer
________________________________
From: Scott Criswell [mailto:scott.criswell at doe2.com]
Sent: Wednesday, March 17, 2010 4:01 PM
To: Grando, John
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] External Wall Calculation
The DOE-2 BDL expression module does not allow parent components to reference keyword values of their child components. Back when the expression module was developed, this limitation was put in place to minimize changes required to the BDL file reading & defaulting mechanism and also to simplify expression dependencies evaluation and minimize the likelihood of circularities defined when two components can each reference data of the other.
The ruleset processing mechanism that provides the foundation of the compliance analysis and QC reporting features of eQUEST does include the ability to reference components in both directions (children referencing parents as well as parents referencing children), but to date this capability has not been extended for use in performing parametric runs or facilitating semi-automated edits to building models.
- Scott
Grando, John wrote:
Hello All,
Does anyone know of a way I can reference a child code word? My specific situation is that I want my infiltration to be controlled via a global parameter that represents the infiltration in terms of CFM/SF of Exterior wall. I want to be able to parametrically change this value so I have to do it in DD Edit. The problem is that infiltration is a zone keyword that is the parent of the exterior wall. It wouldn't be an issue the other way around because I could just use the #P("keyword"). Any ideas on how I can reference the child using DOE2 language?
John Grando LEED AP| Mechanical Engineer
NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof. In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law. If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission. Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege. If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
NOTICE OF CONFIDENTIALITY
This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof. In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law. If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission. Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege. If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100317/28b8bbe3/attachment-0001.htm>
More information about the Equest-users
mailing list