Thanks for your reply,
- This baseline is according to appendix G. If it’s the case of
re-heat, the BTU consumption seems high, (it's an advantage for us)
but how to be sure this is valid.
- If this is the case, how to stop the re-heat.
- There is no space that requires significant cooling all year.
Thanks
On 3/3/10, Karen Walkerman <kwalkerman at gmail.com> wrote:
> with the VAV system, it is likely that your boiler is being used to re-heat
> cool air.  This can account for significant additional boiler energy use, as
> well as boiler energy use in the summer.  If this is an Appendix G baseline,
> take a look at the controls required for water temperature.  Also, due to
> the high increase in boiler energy use between the proposed and baseline,
> I'm guessing there may be a space that requires significant cooling all
> year.  If this is the case, you may be required to provide a separate
> cooling system for this space.
>
> --
> Karen
>
> On Wed, Mar 3, 2010 at 6:33 AM, Paul S. <sep.paul at gmail.com> wrote:
>
>> I've got the result of the end use between baseline and proposed
>> design, everything seems logical except the boilers consumption.
>> Boilers are the same type in the baseline and proposed design.
>>
>> Boilers in the baseline are sized by eQUEST, in the proposed boilers
>> are given calculated by the engineers.
>>
>> The only difference is in the proposed design we used air-cooled
>> chillers and FCU and for the baseline water-cooled and packaged VAVs.
>>
>> Any suggestion about this difference in BTU consumption. And why in
>> baseline desing in June July we have BTU consumption while in the 2
>> designs have same temperatures and same schedules.
>>
>> thanks
>>