[Equest-users] Heat recovery run around loop
    David Bastow 
    dbastow at mcclure-engineering.com
       
    Tue Mar 16 08:21:55 PDT 2010
    
    
  
Nick,
 
In the detailed modeling mode click on the system and then go to the
spreadsheet mode then select energy recovery ventilator drop down menu
and utilize all the inputs in that area, regarding energy recovery
ventilator, to input all your design information.  I have used this
numerous times for the application that you are talking about.  I would
caution you not to just use all the default efficiency numbers that will
show up automatically, but input as close as you can actual design
numbers on efficiency and especially on KW use, that you have involved
in this design process.  You can input the KW use for your pump in the
place of the fan KW or fan and pump KW use together, if that is
applicable.  I have noticed often times that inexperienced modelers
often will just use the KW use default numbers, because it is easy,
rather than really taking the necessary design time to figure out what
the true KW use numbers are actually.  These incorrect input numbers
will many times show the electrical use related to the heat recovery
system to be way higher than they actually are.  This will often make a
very good energy conservation measure, incorrectly, into a real dog.
You should also take real care on how the system is controlled and
should probably run a number of different models, with different control
sequences, to see which control design works best for your particular
heat recovery design.
 
Thanks, 
David A. Bastow 
McClure Engineering, Inc.  
507 Main Avenue West
Post Office Box 1404
Twin Falls, Idaho   83303-1404
<mailto:dbastow at mcclure-engineering.com> 
Web Site:  www.mcclure-engineering.com
<http://www.mcclure-engineering.com/> 
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Nicholas Couture, LEED AP
Sent: Tuesday, March 16, 2010 7:26 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heat recovery run around loop
Hi All:
 
I would like to ask how to model a heat recovery run around loop.
Exhaust air from four air handlers passes over a air to water coil, and
the heat recovered to the water loop is sent to the preheat coils of the
four air handlers.  Keep in mind I have limited experience in the
detailed interface.
 
My first guess is that I would have to create an air to water coil.
Now, how do I connect the exhaust air stream from the four air
handlers... do I set an exhaust amount to each zone??
Then would I create a HW loop connecting the energy recovery coil to the
four pre-heat coils??
 
thanks,
 
Nick Couture, LEED AP
Mechanical Engineer  
 
3555 Veteran's Memorial Highway, Suite M
Ronkonkoma, NY 11779
Tel:  631.981.3990 ext. 230
Fax: 631.981.3971
ncouture at emtec-engineers.com
www.emtec-engineers.com <http://www.emtec-engineers.com/> 
This message is intended only for the personal and confidential use of
the designated recipient(s) named above. This is not in anyway an
official statement of Emtec Consultants or solicitation to buy our
services. Emtec Consultants does not guarantee this Email transmission
to be secure or error-free. Any reproduction or changes to our drawings
and files without the consent of Emtec Consultants is strictly
prohibited.
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/74cb02e0/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 26315 bytes
Desc: email sig.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/74cb02e0/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list