[Equest-users] First Building Performance Simulation
Carol Gardner
cmg750 at gmail.com
Thu Mar 18 15:12:51 PDT 2010
Hi Mike,
You speak of the "model developed by eQUEST assuming a minimum level of
efficiency." There are a couple of things bothering me about this statement.
It is important to realize that eQUEST doesn't "develop" anything, the user
does. This is not to say that eQUEST won't populate fields for you, it will,
and it will suggest defaults for you to use. You, the user, need to
carefully evaluate each and everyone of them, however, or you will not get
what you want.
You don't say exactly what you are trying to find out with the model you
developed. Are you trying to show LEED EB compliance, or evaluate some
individual efficiency measures, or something else? Have you tuned the
results to actual billing data yet? That can be challenging.
Anyway, I'm glad it went well for you so far. Unless you are really, really
good, though, you will probably have some specific questions later. Feel
free to ask us when they come up.
Carol
On Thu, Mar 18, 2010 at 1:19 PM, <mike584595 at aol.com> wrote:
> All:
>
> I have just performed my first simulation using eQuest. I modeled an
> existing building that is about 12 years old. The project went well and
> there were few unknowns because I had free access to the original building
> plans. I have a couple of questions now.
>
> If I understand correctly, the model developed by eQuest assumes a minimum
> level of efficiency that is compliant with ASHRAE 90.1 or California Title
> 24 (see page 4 of the Introductory Tutorial). If this is the case, then it
> is entirely possible (or expected) that the electric or fuel consumption
> will be lower than actual if the original building was not designed to be
> compliant with ASHRAE 90.1 or California Title 24.
>
> Does everyone see it this way a well?
>
> Thanks,
>
> Mike Porter
> Porter Brothers Inc.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100318/539cdcab/attachment-0002.htm>
More information about the Equest-users
mailing list