[Equest-users] [Bldg-sim] (no subject)
Nick Caton
ncaton at smithboucher.com
Mon Mar 29 08:09:05 PDT 2010
The best overall advice I can give is... 90.1 Baseline's aren't supposed
to make sense. ;)
The more nuanced response would be... they aren't supposed to reflect
common design, necessarily. Yes, the system and it's properties vary
with climate, occupancy and building-size/properties... but don't
misinterpret any part of the prescriptive baseline requirements as being
any more than a baseline - an objective set of decisions from which we
can measure a comparative performance level.
To check your findings, as I happen to have 90.1-2004 in front of me,
you are correct assuming your proposed design has electric heating and
assuming you're working under 90.1-2004.
PSZ's are not "preferred" unless the engineer of record decides they
are, regardless of what your baseline happens to be.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
mike584595 at aol.com
Sent: Monday, March 29, 2010 8:47 AM
To: equest-users at lists.onebuilding.org; bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] (no subject)
All:
I am modeling a two story office building that is 20,000 square feet.
The actual building employs a packaged rooftop unit with VAV's and
electric reheat. If I read ASHRAE 90.1 correctly, I am to use System 4
for the baseline modeling. This is in stark contrast to what is
actually installed.
If I am understanding this correctly, do I take from this that Packaged
Single Zone Heat Pumps are preferred in this application?
Thanks,
Mike Porter
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100329/0f5c676e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100329/0f5c676e/attachment-0002.jpeg>
More information about the Equest-users
mailing list