[Equest-users] Summer Overheating Analysis
    Nick Caton 
    ncaton at smithboucher.com
       
    Tue Mar 30 08:16:41 PDT 2010
    
    
  
A fast thought - thought I might be misunderstanding the question...
1. Build an energy model that closely matches the existing building
behavior (matching utility bills/consumption using corresponding
historical weather data).
2a. If there are a significant number of undercooled hours, observe
which zone they are located in
2b. If there are not, uniformly lower cooling capacities across the
board by 10%, 20%... and observe which zones are most prone to being
undercooled.
It would be critical to accurately set the thermostat throttling ranges
and design space temperatures for this study.
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Hind
Dirani
Sent: Tuesday, March 30, 2010 3:14 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Summer Overheating Analysis
Can anyone tell me how to undertake a summer overheating analysis to
identify areas and zones prone to overheating during the hot season?
Any suggestion would be appreciated.
Thanks
Hind