[Equest-users] CAUTION: Variable Speed Drive FPLR???
Eric O'Neill
elo at MichaelsEngineering.com
Thu May 6 12:39:32 PDT 2010
Nick,
I'm not sure I can answer your question. Maybe someone can pick up on
this line of thought though to answer the question.
If you play with the numbers, a PLR of 1.1 is yielding that fan vsd
signal of 1.257. I believe the PLR is calculated as (the current hour's
CFM)/(design CFM). So whatever's going on here is causing the system to
call for (or think it has) a CFM value 10% greater than design. Also,
the function is supposed to set any outputs above the set maximum (in
this case 1) to the maximum, so I'm not sure what about the last day of
the year is causing it to ignore the maximum output value.
When I look at the hourly reports on a system that's using that curve
and getting that error at 12/31/24, my PLR (variable 60) looks fine, and
the CFM is at its minimum. So I don't think it's a real issue. I'm also
not very BDL/DOE2 literate, so I might be looking at this wrong.
Also, if you really wanted a clean ATTN screen, you could just set your
max output from that function to 1.28 ;-)
Cheers,
Eric
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick
Caton
Sent: Thursday, May 06, 2010 12:32 PM
To: Carol Gardner
Cc: eQUEST Users List
Subject: Re: [Equest-users] CAUTION: Variable Speed Drive FPLR???
Thanks Carol!
I'm glad to see some supporting information to assure me this CAUTION is
likely not a big deal, but it still kinda irks me that this is message
is often the only thing between me and a perfectly blank ATTN report in
my models...
If anyone can offer some insight regarding this VSD curve message's
meaning and/or root-causes, I'd be very grateful to either figure out a
way to eliminate these CAUTIONS, or to otherwise be able to sleep at
night knowing I can provide an in-depth response regarding its meaning
and why it's not a big deal and ignore-able.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: Carol Gardner [mailto:cmg750 at gmail.com]
Sent: Thursday, May 06, 2010 12:25 PM
To: Nick Caton
Cc: eQUEST Users List
Subject: Re: [Equest-users] CAUTION: Variable Speed Drive FPLR???
Here you go Nick. This is in your 3-63 data area as DOE-2.chm. There is
tons of info there. Cautions are the least of your worries.
ERRORS Diagnostics deal with problems in the input
that must be corrected before the simulation will execute.
WARNINGS Diagnostics are concerned with input data that
can be used in the simulation but are probably erroneous (such as a
temperature input of 700 instead of 70.0).
CAUTIONS Diagnostics are much less severe than
WARNINGS messages and deal with questionable input value that do not
significantly affect the results of the simulation. This is the default
level.
Regards,
Carol
On Thu, May 6, 2010 at 9:32 AM, Nick Caton <ncaton at smithboucher.com>
wrote:
On many projects, I've run into the following typical CAUTION in my SIM
ATTN report:
**CAUTION***************************************************************
*******
In curve: Variable Speed Drive FPLR the dependent
value
is exceeding the limits.
Value/Min/Max/First time: 1.257 0.100
1.000 12/31/24
It's always referencing this specific library VSD curve, and it always
occurs in the last hours of the very last day of the modeled year. I've
seen it so much I'm pretty certain that particular value 1.257 is always
present too.
What are the implications here to the modeled behavior? Is this caution
something of concern? Is something off with the library curve?
I've always assumed that if something is only off in the last hours of
the modeled year, it shouldn't be a big deal - but it's bugging me that
I'm seeing this come up again and again and I don't know what it really
means...
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
<http://www.smithboucher.com>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100506/dec62f13/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100506/dec62f13/attachment-0001.jpeg>
More information about the Equest-users
mailing list