[Equest-users] Complex chiller/heat recovery/heat pump to model question
Carol Gardner
cmg750 at gmail.com
Fri May 7 09:18:50 PDT 2010
Hi Paul,
I think Matt is on to something. It does have options for both and you can
use Equip Control and maybe Load Management commands. This is heady stuff
for a newbie, however, so I would suggest you hire someone to do a peer
review with you or to work with you.
So, this is an existing building, right? You will also need to bill match,
etc. Where do you actually sit? In Uraguay?
Carol
On Fri, May 7, 2010 at 8:57 AM, Matthew Dubrovich <
mdubrovich at emcengineers.com> wrote:
> Hi Paul,
>
>
>
> Though I haven’t had the opportunity to use either yet, eQuest has options
> for both heat recovery chillers and heat pump chillers, correct? You can
> tie the heat recovery chiller into your hot water loop and it should show
> both a heating savings and condenser fan savings (eliminating those hand
> calcs hopefully). The heat pump chillers can be sequenced through Equipment
> Controls and Load Management to only come on as necessary, after the 165 ton
> chiller is maxed out. Coupling the heat pumps with your hot water system
> may be more of a challenge. Good luck.
>
>
>
> Matt
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Paul Brooks
> *Sent:* Friday, May 07, 2010 9:26 AM
> *To:* Carol Gardner
>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Complex chiller/heat recovery/heat pump to
> model question
>
>
>
> Yes, I did.
>
>
>
> Yes, it is an air-cooled Trane Chiller that has total energy recovery. It
> is a non-US product, made by Trane in Europe.
>
>
>
> The concept is that the chiller provids chilled water, and the energy
> recovery side provides hot water for reheat at VAV boxes when needed.
>
>
>
> In addition, there are two heat pumps (reversible chillers as the
> liturature says)that will pprovide additional capacity to etther the chilled
> water loop or the hot water loop as needed.
>
>
>
> This is for a 110,000 sf high end office building in Uruguay. Uruguay
> is ASHRAE climate zone 3, similar to the US southeast,
> primarily Georga/northern Florida.
>
>
>
> Links to product information:
>
>
>
> Chiller with energy recovery:
> http://doc.trane-eur.com/marketing/cdtrane.nsf/PdfByName/RLC-PRC026-E4_1205.pdf/$file/RLC-PRC026-E4_1205.pdf
>
>
>
> Heat pumps:
> http://doc.trane-eur.com/Marketing/CdTrane.nsf/PdfByName/CG-PRC015-E4_0708.pdf/$file/CG-PRC015-E4_0708.pdf
>
>
>
> I am thinking i will need to do a lot of hand calcs for energy use of the
> chiller and how much "free" heating water I will get. the hard part is
> going to be how to account for saving by not running condenser fans. Yes,
> it will be a challenge to get it through GBCI review, but if the logic is
> sound, it will not be that hard.
>
>
>
> Any suggestions on how to wet up a model in eQuest to minimize amount of
> hand calculations?
>
>
>
>
>
> ------------------------------
>
> *From:* Carol Gardner <cmg750 at gmail.com>
> *To:* Paul Brooks <equestpaul at yahoo.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Sent:* Fri, May 7, 2010 1:54:56 AM
> *Subject:* Re: [Equest-users] Complex chiller/heat recovery/heat pump to
> model question
>
> It looks like you stunned everyone into silence, Paul.
>
> So you have 1) an air cooled chiller, 2) heat recovery sending HW to only
> your reheat coils, 3) 2 air cooled heat pumps that can also provide cool or
> hot water to circulation loops, 4) french hens, and a partridge in a pear
> treee...OOPS, its late!
>
> This looks like entropy to me. Try once more to share all of this. I would
> suggest an itemized list that identifies the equipment type, it's specific
> use, it's model no. etc. and any comments. Maybe an excel spreadsheet would
> work best.
>
> Another issue: this project will be neigh on impossible for a LEED reviewer
> to review, too. That is neither good or bad, it just is.
>
> I will help you as I can, when I can, but I must work for food too. Nobody
> pays me, yet, to help anyone.
>
> Keep the faith,
> Carol
>
> On Thu, May 6, 2010 at 1:47 PM, Paul Brooks <equestpaul at yahoo.com> wrote:
>
> I am modeling a building in Uruguay that has a Trane 165 ton Air cooled
> chiller, (RTAD 165 SE, not available in US.) In addition to air-cooling,
> the chiller has a heat exchanger to recover heat for whatever use you
> want. Obviously the heat recovery means that in the right condisitons the
> condenser fans will not run as much.
>
>
>
> For this application, the heat is to be recovered to provide heating hot
> water VAV box re-heat coils. In addition to this, there are two air cooled
> heat pumps (CXAN 214, not available in US) that are available to augment the
> chiller or the hot wateer loop.
>
>
>
> So, my dilemma, is how to model this in eQuest. I am still more or less a
> novice user. I am in the detail mode, and see that I can do some things
> with condenser water, but then how do I model the condenser fans? How do I
> tie in the heat pump loops?
>
>
>
> Lastly, this is a LEED model. So, any thoughts on how to get data and then
> do hand calcs to prove savings are also welcome.
>
>
>
> Thanks!
>
>
>
> If interestede in seeing info on the equipment, go to Trane-eur.com<http://trane-eur.com/>.
> information is available in english for these models. Your local trane rep
> will probably not be able to help.
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100507/1c65bcbd/attachment-0001.htm>
More information about the Equest-users
mailing list