[Equest-users] Buildign seems to compile, but simulation will not run...HELP!
James Hansen
JHANSEN at ghtltd.com
Mon May 10 09:15:33 PDT 2010
Whenever you get an error midway thru simulation, just view the output
simulation file and scroll all the way to the end for the error that
stopped the processing. In your case, the error is with the DHW pump
being defined but with no return water flow.
Just define a GPM for the DHW Pump 6. Or delete the pump (if there
isn't one).
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul
Brooks
Sent: Monday, May 10, 2010 11:54 AM
To: John Aulbach; eQuest user forum
Subject: Re: [Equest-users] Buildign seems to compile,but simulation
will not run...HELP!
Carol and John:
I checked both the BDL and the INP file, no errors. they are attached
for your review if you can
Thanks!
________________________________
From: John Aulbach <jra_sac at yahoo.com>
To: Paul Brooks <equestpaul at yahoo.com>; eQuest user forum
<equest-users at lists.onebuilding.org>
Sent: Mon, May 10, 2010 11:30:43 AM
Subject: Re: [Equest-users] Buildign seems to compile, but simulation
will not run...HELP!
Paul:
Start in the .BDL file. This is your .INP file as digested by DOE-2 as
it does its error checking before allowing the simulation.
There should be messages telling you what your problem may be. Or send
your .INP and .PD2 files to me and I will give them a quick look.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com <http://www.ptrenergy.com/> | jaulbach at ptrenergy.com
<mailto:%7C%20jaulbach at ptrenergy.com>
________________________________
From: Paul Brooks <equestpaul at yahoo.com>
To: eQuest user forum <equest-users at lists.onebuilding.org>
Sent: Mon, May 10, 2010 8:21:46 AM
Subject: [Equest-users] Buildign seems to compile, but simulation will
not run...HELP!
I have completed a building in DD wizard. I did my initial set-up of
the HVAC system and plants in DD wizard. I completed plant work in
Detail Mode. When I compile the file, I do not get any warnings or
errors. When I ask for a simulation, eQuest seems to do the load calcs
just fine, but when it begins simulation, it states theeis an error, but
I do not know what it is, or how to find it.
Any ideas on what I should do, or where to look for the error?
Thanks
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100510/b27cd4a6/attachment-0002.htm>
More information about the Equest-users
mailing list