[Equest-users] Internal Loads & Choosing the building type
Nick Caton
ncaton at smithboucher.com
Mon May 17 13:07:15 PDT 2010
Omar,
These "typical" values are extracted from libraries when you define such
internal occupancies through the wizards. I do not this information
(ppl/SF, OA/person, etc...) is accessible post-wizards from the eQuest
interface.
I think your options, if you are firmly in detailed mode, are to (A)
look up the values you need in a reference like ASHRAE Fundamentals, or
(B) to create a "dummy" project save and fall back to the wizards,
assign the libray occupancies you want to check up on, and zip back to
detailed mode to extract those internal load & occupancy rates/schedules
you're looking for.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Monday, May 17, 2010 12:21 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Internal Loads & Choosing the building type
Dear all,
The building I'm modeling is a changing room with several WCs and
showers. Where can I choose a typical conditions for such a building
type (assume Gymnasium the being the nearest choice)?
I am in the detailed data mode. I want to view and modify the internal
conditions of the building (typical number of occupants, ,
sensible/latent load from the showers...etc) for a typical gymnasium.
There must be default values associated with each building type.
I hope my question is clear.. Any help is greatly appreciated!
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Chawkatly Building (Valli & Valli), 6th floor
Charles Helou Street, Saifi District
Beirut, Lebanon
Mobile: +961 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0)207 939 0989
Fax: +44 (0)207 939 0981
Website: www.ecoconsulting.net
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/4d590354/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/4d590354/attachment-0002.jpeg>
More information about the Equest-users
mailing list