[Equest-users] exporting hourly results is unavailable
Kelsey VanTassel
KVanTassel at sustaineng.com
Fri May 21 07:39:19 PDT 2010
Hello Nathan,
First you need to set up the hourly report blocks for the variables you want results for.
1. In detail mode, click on the "Project & Site" tab.
2. Under Hourly Report Blocks, right-click on one of the existing blocks and choose "Create another hourly report block".
3. Choose "create from scratch" and name the hourly report block.
4. Pick a category and check at least one variable from the list. Click Done (you can select more variables later).
5. eQUEST will bring you to the hourly report screen. You must assign your newly created report block to an hourly report for eQUEST to tabulate it when the model is run. Hourly reports consist of hourly report blocks which consist of variables, similar to the way annual schedules consist of weeks which consist of day schedules.
6. Click on "Hourly Report". The check boxes on the right show which hourly report blocks are assigned to that hourly report. Check the box next to your new hourly report block. Each hourly report will be exported as a single file containing all of its report blocks and variables so I recommend unchecking any report blocks that you don't really need. You can also create new hourly reports which contain only certain report blocks.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com<mailto:kvantassel at sustaineng.com>
[cid:image001.jpg at 01CAF8C7.90621D90]
We've moved. Please see below for my new contact info.
901 Deming Way, Ste. 201
Madison, WI 53717
608.836.4488 ext. 20| Fax: 608.836.4477
2009 Dane County Small Business Award Recipient
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Friday, May 21, 2010 9:05 AM
To: Nathan Kegel
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] exporting hourly results is unavailable
Look at your .sim file for your project. In the upper right hand corner there is a Hourly Results button. That button sends you to an excel file with all your hourly data.
On Fri, May 21, 2010 at 10:02 AM, Nathan Kegel <NKegel at hga.com<mailto:NKegel at hga.com>> wrote:
New eQuest user just trying to do some preliminary parametric analysis. As part of the analysis I need to export the hourly data to Excel.
I see the "Export Hourly Results" under the File menu is ghosted and unavailable in my model. What steps do I need to take to get this unghosted so I can export the hourly data?
Thanks,
Nathan Kegel LEED AP
Mechanical Engineering
HGA Architects and Engineers
701 Washington Avenue North, Minneapolis, MN 55401
Direct 612.758.4335 | Fax 612.758.9335
nkegel at hga.com<mailto:nkegel at hga.com>
Please consider the environment before printing this e-mail.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100521/d0bd3f8e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 31773 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100521/d0bd3f8e/attachment-0002.jpg>
More information about the Equest-users
mailing list