Open loop geothermal systems are not explicitly model-able within
eQuest, but you're not out of luck. Use another program to determine
monthly or weekly annual ground loop temperature behavior (whoever did
your field sizing/design should be able to produce this), define a
Lake/Well GLHX in detailed mode, and create/assign a schedule of those
temperatures to the GLHX.
For more information, seek my contributions to the following thread in
the archives (I wrote something of a mini-guide to your situation):
Re: [Equest-users] [Bldg-sim] loop to loop heatpump in equest
Sorry to be brief but this should give you a good direction to run in ;)
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jacob
Goodman
Sent: Friday, May 21, 2010 3:07 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Central Geothermal System
I couldn't find any postings on this subject, but maybe I was just using
the wrong search words so here goes. I'm trying to model a geothermal
system that runs open loop from a large aquifer with a 10 deg change in
the water replaced into the aquifer. There will be 2-4 large heat pumps
operating on hot and cold water loops with one heat pump operating
between the two loops. See attached diagram.
The air side of the system will be 4 pipe fan coils since the
maintenance team is familiar with this type of system. There will be a
condensing boiler for backup heating.
* how to simulate an open loop ground well?
* do i need to create hot, cold and GSHP loops under water-side
HVAC...if so how do I tie them together?
Any tips on how to model this system will be very helpful, Thanks much!
Jacob Goodman , LEED AP
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100521/5e5ec6bf/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100521/5e5ec6bf/attachment-0002.jpeg>
More information about the Equest-users
mailing list