[Equest-users] Electricity consumption by CHILLER
Grammy
grammy.hkust at gmail.com
Fri Nov 5 04:17:18 PDT 2010
I am also confusing this problem, and I strongly recommend you to read the
DOE-2 engineering manual, verison 2.1A, and DOE-2.2 volume 4, which can be
downloaded from eQuest web site.
On page V.35 - V.38, engineering manual, it introduces the electric
calculation of chiller, and on page 265, volume4, it introduces the chiller
variable list number, you can export the hourly data in eQuest and
calculated by hand. I am lost at this step. As i know at this place, there
is something you need to notice, the unit of assign loading (1) shall be
BTU, and electric demand (12) may be kW, then I still can't get the right
number, if you get it, please let me know how.
On Fri, Nov 5, 2010 at 8:04 AM, Ana N. <ananeddav at hotmail.com> wrote:
>
> I am trying to calculate/estimate the electricity consumption by a
> chiller based on hourly outputs.
>
> First, I plugged the cooling coil load on loop and corrected EIR in the the
> equitation
> Elec= CAP hour* EIR*EIR(t1,t2)*EIR(PLR,dT)/3413 Btu/kW
>
> but the calculated annual electricity consumption was not even close to
> the numbers reported under Space Cooling Enduse.
>
> Then, I used PLR and operating chiller capacity at current condition to
> calculate CAP hour (instead of using the cooling coil load on loop), but
> calculated numbers did not make any sense.
>
> Has anyone done similar calculations? I am sure I am missing something very
> simple here, but what?
>
> Any suggestions are very appreciated
>
>
> Ana
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/b1c7942d/attachment-0001.htm>
More information about the Equest-users
mailing list