[Equest-users] HVAC System 7 in eQUEST
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Wed Nov 24 09:54:55 PST 2010
Praveen, System Type 7 is actually VAV w/reheat, chillled water
coils....etc.
The "packaged" that is printed in front of it is a "typo" in the
Standard. You should use the non-packaged option for your baseline model.
Pasha
On Wed, Nov 24, 2010 at 9:19 AM, Rob Hudson <rdh4176 at gmail.com> wrote:
> use VAV type system. Typically packaged is for DX units. i am doing the
> same thing in a model right now as well.
>
> On Wed, Nov 24, 2010 at 10:36 AM, Praveen Jain <praveenjain83 at gmail.com>wrote:
>
>>
>> Dear all
>>
>> As per ASHRAE 90.1 HVAC System 7 is Packged rooftop VAV with Reheat and
>> cooling type is Chilled water.
>> How can we model above HVAC System in eQUEST.
>> If I choose Cooling source as Chilled water coils than it donot show
>> any Packaged system in System Type drop-down.
>> --
>> With Thanks and Regards,
>> Praveen K. Jain
>> Roorkee
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
> --
> Rob Hudson
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101124/f304baf5/attachment-0001.htm>
More information about the Equest-users
mailing list