[Equest-users] Water Source Heat Pump Efficiencies
Kelsey VanTassel
KVanTassel at sustaineng.com
Fri Oct 1 07:07:12 PDT 2010
No, you are right, there is nothing listed in the tables for water-source heat pump greater than 135,000 Btu/h. I think that's when you go to the water-chilling packages table and start looking at the minimum efficiencies for water-cooled chillers. That wouldn't cover the heating mode, though. Maybe someone else knows for sure.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com<mailto:kvantassel at sustaineng.com>
608.836.4488 ext. 20 | Fax: 608.836.4477
Sustainable Engineering Group
901 Deming Way, Suite 201
Madison, WI 53717
www.sustaineng.com<http://www.sustaineng.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Daniel Deese
Sent: Friday, October 01, 2010 8:52 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Water Source Heat Pump Efficiencies
Hi all,
I know they always say there's no such thing as a stupid question, but I've been looking through ASHRAE 90.1 table 6.8.1 as well as I know how, and I cannot find the required efficiency rating for a water source heat pump with a capacity greater than 135,000 BTU/hr. We're trying to model Multistack heat pump/chillers, and we're using the 70-ton model, which correlates to about 840,000 BTU/hr.
Has anyone ever modeled a water source heat pump larger than 135 MBH, and if so, which efficiency did you use? I know I'm absolutely horrible at where's waldo, so there's a good chance I've just overlooked it. Any help or advice is as always appreciated. Thanks.
daniel
Daniel I. Deese, EI| CRB Consulting Engineers |
1255 Crescent Green, Suite 350 | Cary, NC 27518 |
P: 919-852-5443 | F: 919-852-5454 | X: 4543
Email: daniel.deese at crbusa.com<mailto:daniel.deese at crbusa.com>
________________________________________________________________________________________
This document may contain confidential information and is intended for use by the addressee only. If you are not
the intended recipient, please do not transmit, copy, disclose, or utilize this communication in any manner. If you
received this message in error, please notify the sender immediately and delete this message.
ü Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101001/165558ac/attachment-0001.htm>
More information about the Equest-users
mailing list