Not stupid at all, If you have your altitude set to anything but 0 eQUEST
will adjust your cfm accordingly. I always go in and set it manually to
zero. I think it reads what it is off the weather file.
Carol
On Fri, Oct 8, 2010 at 6:54 AM, Christian Stalberg <
cstalberg at naturalintelligence.us> wrote:
> They say no question is a stupid question.
>
> Why is my zone level supply flow cfm reported value in the SV-A report
> higher than my overall design flow (ASSIGNED-FLOW) value? The
> system sizing ratio is set at 1.00 (default).
>
> Thanks in advance.
>