[Equest-users] design flow input vs. SV-A supply flow reporting
Nick Caton
ncaton at smithboucher.com
Fri Oct 8 09:55:13 PDT 2010
First, thanks to Carol for elevating my understanding of elevation in
eQuest (see what I did there??? it's a Friday alright)...
That was always a mystery to me and I'm finding elevation is indeed the
source of my CFM's bumping up (not doubling though) on at least one
previous project.
That said, Paul:
I'm pretty sure you can expect any entered zone-level design airflows
(including exhaust) to potentially override or otherwise mess with
system level airflow inputs if/when they ever sum to be larger.
If you specify a system-level design airflow which is below what the
loads require but not in conflict with any zonal inputs, eQuest appears
to simply adjust upwards for elevation if >0, then upward to the limits
of your entered max-flow-ratio, then follows through and spits back
unmet load hours in the results, as you'd expect, but importantly will
not inflate your system's design CFM beyond the max-flow ratio to
compensate for unmet loads - so it may be good to know whatever is
doubling the specified CFM in your model is probably not related to your
load inputs.
Oh yeah, the system sizing ratio (found on the first tab opening any
airside system) will inflate your airflows too if it's above 1.0 -
better check that.
Sidenote: The fasted way I know of to check resulting airflow results is
to be aware of the summary tab. After a calc, highlight a system within
(or the project at the top of) the component tree under air-side HVAC
and click the summary tab underneath the toolbars.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matthew
W. Higgins
Sent: Friday, October 08, 2010 10:54 AM
To: Paul Diglio; Carol Gardner; cstalberg at naturalintelligence.us
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] design flow input vs. SV-A supply flow
reporting
Depending on your system type (VAV) I've found that you need to ensure
your Min and Max flow ratios are set at 1.0 for each system, if
appropriate. While the system sizing ratio is one thing, flow ratios are
another.
But maybe you've tried that already, I don't know...
Matthew Higgins, ASHRAE-HBDP, LEED-AP
Energy Engineer
Bridgers & Paxton Consulting Engineers, Inc.
4600-C Montgomery Blvd. NE
Albuquerque, NM 87109
505-883-4111
505-888-1436 Fax
mwhiggins at bpce.com
www.bpce.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul
Diglio
Sent: Friday, October 08, 2010 9:06 AM
To: Carol Gardner; cstalberg at naturalintelligence.us
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] design flow input vs. SV-A supply flow
reporting
Carol:
I am having the same problem with airflow almost double from what I
specified. I tried the altitude correction and that did not help.
Does the zone air flow and exhaust rate take preference over the fan
flow parameters?
Thank you,
Paul Diglio
________________________________
From: Carol Gardner <cmg750 at gmail.com>
To: cstalberg at naturalintelligence.us
Cc: equest-users at lists.onebuilding.org
Sent: Fri, October 8, 2010 9:33:46 AM
Subject: Re: [Equest-users] design flow input vs. SV-A supply flow
reporting
Not stupid at all, If you have your altitude set to anything but 0
eQUEST will adjust your cfm accordingly. I always go in and set it
manually to zero. I think it reads what it is off the weather file.
Carol
On Fri, Oct 8, 2010 at 6:54 AM, Christian Stalberg <
cstalberg at naturalintelligence.us> wrote:
They say no question is a stupid question.
Why is my zone level supply flow cfm reported value in the SV-A report
higher than my overall design flow (ASSIGNED-FLOW) value? The
system sizing ratio is set at 1.00 (default).
Thanks in advance.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101008/85e2bd12/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101008/85e2bd12/attachment-0001.jpeg>
More information about the Equest-users
mailing list