[Equest-users] (no subject)
Eddie Corwin
ecorwin at altanova-energy.com
Tue Oct 19 08:27:36 PDT 2010
You can not make a "Doughnut" zone. you will need to separate the perimeter
zone into two or more zones. Using the "Core/Shell Zoning pattern that is
available in the wizard works well.
________________________________
From: Erik Weiss <ew0187 at gmail.com>
To: equest-users at lists.onebuilding.org
Sent: Tue, October 19, 2010 11:22:08 AM
Subject: [Equest-users] (no subject)
I am creating a 20 floor building and the core is defined. i am trying to create
the zones within the core and the large single zone surrounding the core. I am
unable to create 1 single zone surrounding the core because the wizard does not
allow you to select the same vertex twice in a single zone. Is there anyway
around this