Hi Mikhail,
It is not a straight-forward process in eQuest but it can be done. If I
were in your shoes however I wouldn't separate these two constructions in
eQuest. I would do some pre-processing of my inputs on my own with a
pencil & calculator. My approach would be to calculate the area-weighted
average for my U-value of the wall based on the following:
(U-value underground const * X% of total wall area) + (U-value above-ground
const * 1-X% of total wall area) = Model Wall U-value for my simplified
input value.
Where you "manipulate" or process your input data outside of eQuest using
sound engineering & mathmatically theory you can simplify your input process
significantly. The challenge & balance to remember is that we have to be
careful not to over-simplify our input assumptions too much if they may skew
our model results in anyway. Just like life, good simulation skills are a
balancing act.
Also, my Father speaks Russian and if you need more detailed assistance with
your energy modeling & eQuest skills I could have him translate for me from
English to Russian if this would help you.
Pasha
2010/10/21 Grammy <grammy.hkust at gmail.com>
> Read DOE2.2 Volume, you can build that wall separately, some underground -
> you can see it in eQuest 3D view, in green color, and some part is upground.
> Just cut the wall and input the accurate coordinate in detail mode.
>
> 2010/10/21 Самолётов Михаил <samoletov.mikhail at bt-comfort.ru>
>
>> I am modeling a two-storied building. It has one floor that is
>> situated partly below the grade. Upper part of this floor lying above the
>> grade and contains few windows. I have not found how to model this in
>> eQUEST. I have tried to make 2 floors instead of the lower floor: one is
>> below and other is above the earth surface, but then they have a ceiling
>> between them! It is wrong, I think! I do not need this additional ceiling in
>> the model.
>>
>>
>>
>> Is there anybody who speak Russian here? :)
>>
>>
>>
>> Sincerely yours,
>>
>> Mikhail Samoletov
>>
>> Chief engineer of
>>
>> *"Numerical Simulation Department"*
>>
>> *TECHNIQUE BUREAU*
>>
>> Cvetochnaya str, 25"Zh", 196084 St.Petersburg, Russia
>>
>> www.bt-comfort.ru
>>
>> phone/fax +7 (812) 318-50-30
>>
>> mob. +7 (931) 244-83-77
>>
>>
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101021/e32d5c43/attachment-0001.htm>
More information about the Equest-users
mailing list