[Equest-users] Appendix Tabel G3.1.1 1 Correspondence
Carol Gardner
cmg750 at gmail.com
Mon Oct 18 09:55:27 PDT 2010
Rick,
The PFP box is just the zone delivery box for your VAV system. Use the
efficiency for the corresponding size of your system, not the box.
Best,
Carol
2010/10/17 YinRic <cesseric at hotmail.com>
> Hi Users,
>
> I am not an HVAC expert, and I have a basic question to ask, though it is
> not quite related to equest itself:
>
> If the Baseline HVAC system type is "System 6-Packaged VAV w/PFP Boxes",
> which one from Table 6.8.1A-G shall I use to determine the minimum
> efficiency?
>
> After review of EAc1 from GBCI, it is stated that my COP/EER input is
> inconsistent with Table 6.8.1--"The applicable capacity ranges for the
> systems used in the Baseline and Proposed Case shall be consistent with the
> ranges listed in Tables 6.8.1A through 6.8.1G." It seems to me that a
> wrong table is used as reference.
>
> Thanks in advance!
>
> Rick
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101018/38491e7f/attachment-0002.htm>
More information about the Equest-users
mailing list