Alex,
To add to Eddie’s comment, the LS-B report shows the space peak loads by component. So you can look at the window glass + frame conduction load and the window glass solar load independently.
John
John T. Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated Services I 617.658.9008 tel I 617.244.3753 fax I One Gateway Center Suite 506, Newton MA 02458 I www.bvhis.com<http://www.bvhis.com> I Hartford ● New Haven ● Boston
size=2 width="100%" align=center tabindex=-1>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eddie Corwin
Sent: Thursday, October 21, 2010 4:17 PM
To: equest-users
Subject: Re: [Equest-users] Peak Loads: PS-E and SS-J and LS-C
LS-B will give you the heating and cooling peak load for individual spaces. LS-C will give you the same information, but for the entire building.
__________________________________________________________
Eddie Corwin, Energy & Sustainability Engineer
ALTANOVA - www.altanova-energy.com
41-41 24th Street - 4th Floor - Long Island City, NY 11101
T: (347) 410-9049
E: ecorwin at altanova-energy.com
________________________________
From: Alex Krickx <akrickx at seriousmaterials.com>
To: equest-users <equest-users at lists.onebuilding.org>
Sent: Thu, October 21, 2010 3:26:20 PM
Subject: [Equest-users] Peak Loads: PS-E and SS-J and LS-C
Hi all,
I am interested in determining Peak Cooling reductions (in KW) associated with a window retrofit. I don’t have all of the HVAC information, so I am hoping to show the space-level savings (instead of system- or plant-level). I’m trying to figure out which report I can pull Peak Cooling Load- so far looking through the archives and LS-C seems most appropriate. Since I want to ignore the system and plant and only look at the impact of the windows on the building space load, is this the right place to pull peak load from?
Thanks,
Alex
Alex Krickx
Building Energy Specialist
[cid:image001.jpg at 01CB7144.7CFB7440]
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged attorney-client communications or attorney work product and/or proprietary and confidential. If the reader of this message is not the intended recipient then you have received it in error and any review, distribution or copying of this message is prohibited and you are to notify us immediately by reply e-mail and delete the original message immediately.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101021/480e0cf7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5602 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101021/480e0cf7/attachment-0002.jpg>
More information about the Equest-users
mailing list