[Equest-users] Review Requested
Eddie Corwin
ecorwin at altanova-energy.com
Thu Sep 9 12:26:03 PDT 2010
In both of your HVAC systems you have "Outdoor Air From System" object
specified. In most cases, you will want to leave this object blank. The only
time would want to use that object if, for example, you were taking the return
air from one system, and using it in another, separate, system. I am pretty
sure that in your case, especially in the labs, all of the air will be coming
from the outside, or will be recirculated within the same system.
If you reset those values to their default you get much better cooling results,
but you also get heating in the summer, which is another issue you need to look
at in more detail. The "Outdoor Air From System" object is found in your HVAC
system --> Outdoor Air --> Outdoor Air and Economizer
-Eddie
________________________________
From: "equest-users-request at lists.onebuilding.org"
<equest-users-request at lists.onebuilding.org>
To: equest-users at lists.onebuilding.org
Sent: Thu, September 9, 2010 3:03:35 PM
Subject: Equest-users Digest, Vol 30, Issue 13
Note: Forwarded message is attached.
Send Equest-users mailing list submissions to
equest-users at lists.onebuilding.org
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
or, via email, send a message with subject or body 'help' to
equest-users-request at lists.onebuilding.org
You can reach the person managing the list at
equest-users-owner at lists.onebuilding.org
When replying, please edit your Subject line so it is more specific
than "Re: Contents of Equest-users digest..."
Today's Topics:
1. LEED compliance new version of eQuest (Peter Hillermann)
2. LEED compliance new version of eQuest (Peter Hillermann)
3. Re: Review Requested (Umesh Atre)
4. Re: Infrared Heaters (Peter Hillermann)
5. Re: Review Requested (Paul Diglio)
6. Re: Reduction of window area in detail mode! (Arunabha Sau)
7. Re: Infrared Heaters (Peter Hillermann)
8. Re: Infrared Heaters (Nick Caton)
9. Re: Infrared Heaters (Peter Hillermann)
10. Re: Review Requested (Umesh Atre)
11. Re: Floor Slab F-factor (Jeremy Poling)
12. Re: Infrared Heaters (Charles Land)
_______________________________________________
Equest-users mailing list
Equest-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/a9e68e8d/attachment-0001.htm>
More information about the Equest-users
mailing list