[Equest-users] HELP - Drawing accurate building footprint and generating correct roof type
Nick Caton
ncaton at smithboucher.com
Wed Sep 8 07:17:18 PDT 2010
Hi Vaughn,
1. You can define 3 separate shells easily in the DD wizards.
Start by finding/making a Cad file containing each shell footprint in
geometric relation to each other, finish out your first shell
(geometries, scheduling, constructions, LPD, etc) as you normally would,
then start another by copying the first and reference the same file when
tracing out new shells. This will have the advantage of creating
additional exterior walls where you need them (stairwell), but you
should probably include the boiler rooms in the shell they're attached
to as unconditioned spaces, to get those losses correctly modeled.
2. You may want to define the exterior stairwells as a series of
building shades (just the landings would be fine) in detailed mode after
the wizards. This will mitigate solar loads such exterior walls would
not actually see. This may also cover the "gaps" between the shells if
you are concerned aesthetically about "one roof."
3. The advice I generally follow regarding custom/tilted roofs is
that it's usually not worth the effort - flat roofs can often
approximate thermal interactions to a plenum space quite well enough.
That said, if your heart is set on custom tilted roof shapes - you're
going to need to resolve to spend some time after the wizards crunching
numbers in detailed edit mode to modify the vectors of the
wizard-generated polygons. I'd recommend searching the archives for
more procedural info or starting a separate query if you get hung up in
this.
4. Your concern that the roof shape will affect the (exterior?)
stairwells' behavior gives me pause however... not sure what you mean
there. Defining 3 separate, non-touching shells will account for the
additional exterior walls you'd want to model if that's what you mean...
Someone wise once told me that "accuracy" is not nearly as important as
understanding "accurate enough."
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Synergy
Team
Sent: Tuesday, September 07, 2010 10:22 AM
To: eQUEST-users at onebuilding.org
Subject: [Equest-users] HELP - Drawing accurate building footprint and
generating correct roof type
Greetings All,
I am attempting to model a two-story multi-family structure with 16
apartment units, 8 per floor. The building is symmetrical with 8 units
in the middle section (4 units per floor) and 4 units (2 units per
floor) on either side. Despite being one structure, the plans indicate
that it is actually divided into 3 separate Thermal Shells because there
is a stairwell and an unconditioned boiler room in between each of the
three "volumes". Thus far, I have only been able to model buildings in
eQUEST as one box or volume. I would like to be able to model this
structure accurately (as three separate thermal shells under one roof).
Does anyone know how to do this? Also, I continue to have problems
generating the roofs accurately. I will draw a box-like building
footprint and when the roof generates in equest, It is often times
pitched in the wrong direction or does not have the correct
relationships between roof elements. Can anyone help me use the custom
roof footprint option? I have "fudged" some eQUEST models in the past
where I thought it would not effect the accuracy of the model much,
however, I am hesitant to fudge this model as such being that there are
four long walls in this building that will losing considerable heat to
the exterior stairwells and unconditoned boiler rooms (in between the
volumes). Any suggestions would be greatly appreciated. Thanks.
Regards,
Vaughn Slovak
Architectural Designer
Synergy Design
p.845.255.1733
f.845.255.1694
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100908/d078750c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100908/d078750c/attachment-0002.jpeg>
More information about the Equest-users
mailing list