[Equest-users] Heat Control Reset
Patrick O'Donnell
pco at MichaelsEngineering.com
Wed Sep 15 09:08:49 PDT 2010
Bill,
Thanks for the advice. I found I could create the schedule that way,
but I am finding that the cooling control of PVAV is really what
controls the heating. Making adjustments on the heating controls really
only changes the sizing/responsiveness of heating air at the central
level during winter; you cannot manipulate heating DA temp setpoint from
the heating controls only from the cooling control min and max reset
range, if that makes sense.
Anyways, cheers,
-Patrick
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Sent: Tuesday, September 14, 2010 10:39 AM
To: Patrick O'Donnell; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Heat Control Reset
Patrick,
Create the reset schedule you want (of TYPE=RESET-TEMP), then select it
in the HEAT-RESET-SCH field by right-clicking, selecting "Edit/View User
Default" and selecting your new schedule as the User-Defined Default
Value. I think you can follow this process for any field that is
grayed-out with "n/a", though you may not get meaningful results if you
override a field when it really is not applicable.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Patrick
O'Donnell
Sent: Tuesday, September 14, 2010 11:12 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heat Control Reset
Hi all,
I am using a PVAV with HW baseboard heating and would like to implement
a discharge air temperature heating control reset at the central level
(using the AHU's furnace). I can get the option of selecting the
"Reset" heating control option by controlling my cooling based off the
Warmest zone and plugging in a Hot Deck Max Leaving Temp. The thing is
there is no further specification of this control such as what OA temp
conditions will control the reset and running hourly reports show that
this Reset heating control isn't really doing anything. Am I missing
something here or is this heating control not properly supported in the
newest version of eQuest?
Any help would be much appreciated, thanks!
-Patrick