[Equest-users] Aircraft Hanger Modeling
    MatthewRLarson at Eaton.com 
    MatthewRLarson at Eaton.com
       
    Mon Apr  4 13:34:33 PDT 2011
    
    
  
I don't have a lot of experience with Natural Ventilation but it seems
to be dependent on the thermal conditions in the zone.  You can specify
"open" for an hour but if natural ventilation doesn't hold the zone
thermostat setpoint, "program reverts to mechanical cooling" as stated
in the help file.  Whether this means the Natural Ventilation is then
closed, I don't know.  Basically, Natural Ventilation may work in this
case but I would make sure the natural ventilation is operating how you
would like the hangar doors to be simulated with hourly reports.  It
seems to me though that specifying Internal Load Infiltration would be a
better option since the hangar doors are not controlled or open/closed
based on thermal conditions in the zone.
 
Thanks,
 
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems 
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239
MatthewRLarson at Eaton.com 
www.eaton.com/energysolutions  
 
 
From: Arpan Bakshi [mailto:arpanbakshi at gmail.com] 
Sent: Monday, April 04, 2011 2:10 PM
To: nabil koubaa
Cc: Larson, Matthew R; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Aircraft Hanger Modeling
 
Have you looked into using the natural ventilation option with either
air change or sherman-grimsrud method?
 
Switch to Detailed Mode > Air-Side HVAC > Outside Air > Natural
Ventilation
 
 
On Mon, Apr 4, 2011 at 3:57 PM, nabil koubaa <nkoubaa at gmail.com> wrote:
thank you for your help Matthew this is great information exactly what I
was looking for.
 
On Mon, Apr 4, 2011 at 3:54 PM, <MatthewRLarson at eaton.com> wrote:
If you go to the hangar space properties under Internal Loads and the
Infiltration tab, you can apply an hourly schedule there.  Below is a
screen shot of the infiltration tab and the help file for the Schedule.
I believe this has to be done in detailed mode, not wizard mode.  Let me
know if you want to see an example schedule or something.
 
Error! Filename not specified.
 
Thanks,
 
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems 
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419 <tel:303%20328-3419> 
mobile: +1 303 668-2511 <tel:303%20668-2511> 
fax: +1 303 974-1239 <tel:%2B1%20303%20974-1239> 
MatthewRLarson at Eaton.com 
www.eaton.com/energysolutions  
Error! Filename not specified.
 
From: nabil koubaa [mailto:nkoubaa at gmail.com] 
Sent: Monday, April 04, 2011 1:47 PM
To: Larson, Matthew R
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Aircraft Hanger Modeling
 
Matthew,
using the infiltration could be the way to go, I know that it is
possible to create a parametric run for infiltration but is it possible
to put it on a schedule?
thank you
 
On Mon, Apr 4, 2011 at 3:38 PM, <MatthewRLarson at eaton.com> wrote:
Just a thought, but could you treat it as infiltration.  Under Internal
Loads,  specify a high infiltration rate and create an infiltration
schedule based on hangar doors opening and closing at different times
during the day.  If anyone has any other ideas, please share.
 
Thanks,
 
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems 
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419 <tel:303%20328-3419> 
mobile: +1 303 668-2511 <tel:303%20668-2511> 
fax: +1 303 974-1239 <tel:%2B1%20303%20974-1239> 
MatthewRLarson at Eaton.com 
www.eaton.com/energysolutions  
Error! Filename not specified.
 
From: equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] On Behalf Of nabil koubaa
Sent: Monday, April 04, 2011 12:20 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Aircraft Hanger Modeling
 
Hello all-
I'm modeling an aircraft hanger and I'm not sure how to model hanger
doors being opened and closed at different times per day.
 
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-- 
 
 
Arpan Bakshi  LEED AP BD+C
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110404/db49f73e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110404/db49f73e/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list