[Equest-users] question about SIM output data (building load and HVAC load)
David Eldridge
dse at grummanbutkus.com
Tue Apr 5 16:20:25 PDT 2011
The LS-A, -B, -C reports show the gains to the space(s) from envelope,
occupants, lights, equipment, infiltration, etc. These are reported at the
time of the greatest cumulative effect during the simulation. (W or BTU/hr)
As you mention, the SS series of reports shows the energy used to operate
the systems, including equipment efficiencies, outside air, etc. Reheat
also could add significantly to SS report energy compared to the space gains
from the LS reports.
David
*
*
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
*Grumman/Butkus Associates*
*
*
*From:* equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] *On Behalf Of *xiaoyang shi
*Sent:* Tuesday, April 05, 2011 4:11 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] question about SIM output data (building load and
HVAC load)
Hi folks,
Here is a question.
>From the SIM LS-F (Building Monthly load component), and calculate some
simple steps by ourselves, we can know the yearly building heating load is 6
kwh/ft2
Meanwhile, From SS-D (building HVAC system load summary), we can know the
yearly HVAC heating load is 25 kwh/ft2
There is a 19 kwh/ft2 difference between each other.
Could I ask what the reason is? (Note: I know this is the HVAC system
efficiency, but could I know more detailed quantitive reasons? ) For
example. the duct heat loss, the returning air heat loss. (Can we get these
data from eQUEST output?, like the heat loss from the wall, window, roof,
ground...)
Do you guys know any paper or documents about this question?
Thank you very much.
Sincerely yours,
Yang
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110405/45a0385e/attachment-0002.htm>
More information about the Equest-users
mailing list