[Equest-users] Change underground wall to above ground
    Nick Caton 
    ncaton at smithboucher.com
       
    Fri Apr  8 17:10:17 PDT 2011
    
    
  
Hi Sheri,
 
I'm not sure which instructions you're referring to (there's been too much!), but if you're trying to achieve something like the exterior-plenum-wall on a below-grade shell like below, check out this step-by-step instructional to change an exterior wall to an interior surface: http://onebuilding.org/wiki/doku.php/convert_an_exterior_surface_to_an_interior_surface_detailed
 
The below is achieved following the same procedure in concept, only instead of creating a new interior wall to replace the exterior wall, it's creating an exterior wall to replace the underground surface.  Give it a try - after doing this once it'll take you a minute or less in the future!
 
(PS: ignore the adiabatic wall on the right - that was helping another fella out just now...)
 
 
 
Bonus challenge!:  
After reading my how-to and conquering the above, I'll bet you can figure out the extra step to accomplish sloped basement exposures, just like the ever-impressive Bill Bishop:
 
 
(hint if you need it - Bill made it look easy in the archives...)  
 
If you can pull that off, please don't hesitate to flex your sexy modeling muscles and show off the results ;).  
 
Best of luck!
 
~Nick
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sheri
Sent: Wednesday, April 06, 2011 12:14 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Change underground wall to above ground
 
I have a 3 story building with one floor ½ below ground. I have gone through the archives & found instructions from Nick Caton on how to design the wall so part is below ground & part is above ground, but when I initially did this I set the whole shell underground. I need to change the portion above the ceiling to above ground instead of below ground & then I can do the rest of the wall like Nick instructed. Any assistance would be greatly appreciated!!!!
 
Thank you,
 
Sheri Rice,
Assistant General Manager
Fire & Ice Geothermal, LLC
198276 E County Road 41
Woodward, OK 73801
580-256-9439 Voice
580-256-7080 Fax
580-216-1005 Cell
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110408/d1a67b8b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 58330 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110408/d1a67b8b/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110408/d1a67b8b/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20723 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110408/d1a67b8b/attachment-0005.jpeg>
    
    
More information about the Equest-users
mailing list