Hi Kathiresan!
 
If you have 100 spaces that you can state are identical in every
practical sense (think hard about envelope loads/orientation, interior
loads and scheduling), 
And every FCU is identical in every practical sense (considering
capacity, part load curves, controls, scheduling, etc.), 
And heat transfer between other interior spaces is not a big deal,
Then I'd propose the following wizard-centric approach:
 
1.       Create 1 shell in the wizards to represent your typical space.
2.       Define adiabatic surfaces for all footprint perimeters (see
attached post from last week), floor and roofs that are interior
partitions 
3.       Assign a shell multiplier of 100 (first shell screen in DD
wizards)
4.       When defining your HVAC system, enter any inputs you don't want
auto-sized by a factor of 100 (heating/cooling/CFM capacities).  Specify
any non-capacity inputs (such as oversizing factors, rated efficiencies
and thermostat setpoints) as though you were defining a single unit.
 
What you'll get is a very trim, small model that handles the x100
multiplier very efficiently during the simulation.  You'll have a single
system sized to handle all 100 spaces at once, riding the same set of
performance curves and operating under a single set of schedules.  In
evaluating/refining your model, keep the factor of 100 in mind.
Example: if the system summary reports 180,000 CFM, an individual unit's
CFM is really (180,000/100)= 1,800 CFM.  
 
I'd advise investing some of the time you would saved with this approach
to double-check any auto-sized pump/loop energies correctly reflect the
x100 FCU's.  Also consider extra scrutiny for any library-sourced
performance curves used (if you aren't defining your own already), as a
small difference from reality can become a large one when dealing with a
x100 multiplier.
 
Best of luck!
 
~Nick
 
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
cic at jci.com
Sent: Monday, April 11, 2011 3:54 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] (no subject)
 
Hi, 
Just want to know if there are 100 FCU's in a building & follow one
schedule and have similar capacity. Do we need to model 100 FCU's? or
any other way to simplify it? 
Assume thermal properties remain same for all. 
Thanks, 
Kathiresan
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110411/9db6c407/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110411/9db6c407/attachment-0002.jpeg>
-------------- next part --------------
An embedded message was scrubbed...
From: "Nick Caton" <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Change underground wall to above ground
Date: Fri, 8 Apr 2011 19:10:17 -0500
Size: 127278
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110411/9db6c407/attachment-0002.eml>
    
    
More information about the Equest-users
mailing list