[Equest-users] U value temperature dependence in eQUEST
    Brian Fountain 
    bfountain at greensim.com
       
    Mon Apr 18 12:00:21 PDT 2011
    
    
  
Unfortunately, the envelope loads are calculated in the Loads routine, 
in advance of the system response calculation by the System (and Plant) 
routine.  So, if the zone temperature is considerably different than the 
space temperature (used for the loads calculation), there will be a 
difference in the envelope driven heating/cooling requirement.
It is an iterative process (in each time step) to calculate the actual 
space temperature.  DOE-2 (neither 2.1 nor 2.2) do not do this iterative 
process.  If it is important -- that is what EnergyPlus does.
On 4/18/2011 2:48 PM, Harrity, Sean wrote:
>
> Hi,
>
> Does anyone know if and how eQUEST accounts for the temperature 
> dependence of U values? For instance, some manufacturers specify a 
> summer design condition U value that is different from a winter design 
> condition U value. Ideally I would like to have eQUEST calculate the 
> hourly U value based on the hourly temperature to get accurate skin 
> loads throughout the whole year. If anyone knows how this can be done, 
> please let me know.
>
> Thanks,
>
> Sean
>
> *Sean Harrity* |*Mechanical Engineer
> *Phone: 212-615-3923 | Fax: 212-615-3700
> sharrity at cosentini.com
>
> *Cosentini Associates - A Tetra Tech Company
> *Two Pennsylvania Plaza - Third Floor - New York, NY 10121
> www.cosentini.com <http://www.cosentini.com/>
>
>
> NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if 
> any) are intended solely for the use of the addressees hereof. In 
> addition, this message and the attachments (if any) may contain 
> information that is confidential, privileged and exempt from 
> disclosure under applicable law. If you are not the intended recipient 
> of this message, you are prohibited from reading, disclosing, 
> reproducing, distributing, disseminating or otherwise using this 
> transmission. Delivery of this message to any person other than the 
> intended recipient is not intended to waive any right or privilege. If 
> you have received this message in error, please promptly notify the 
> sender by reply E-mail and immediately delete this message from your 
> system.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1209 / Virus Database: 1500/3582 - Release Date: 04/18/11
>
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1209 / Virus Database: 1500/3582 - Release Date: 04/18/11
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110418/cd366e8c/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list