[Equest-users] OA hourly data
Haddad, Kamel
Kamel.Haddad at NRCan-RNCan.gc.ca
Tue Apr 19 10:06:39 PDT 2011
Rohini, I meant to indicate to use the smallest number that is > 0. A
zero value will make DOE-2 use the default.
Kamel Haddad.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of R B
Sent: April 19, 2011 12:40
To: eQUEST Users List
Subject: Re: [Equest-users] OA hourly data
Kamel, Bill,
Thanks for the reply. I changed the OA cfm for all the zones to 0. Now
in the SV-A report the zone OA is showing as zero but the system OA
ratio is 0.2 and the custom hourly report variables (ratio of outside
air to supply flow - Var 39, and the minimum OA damper position - Var
80) are still varying from 0.21 to 0.56. Not sure from where eQuest is
getting 0.2 value or these other values in the hourly report.
Does VAV have a default minimum outside air that cannot be overwritten?
Thanks
-Rohini
On Tue, Apr 19, 2011 at 10:16 AM, Haddad, Kamel
<Kamel.Haddad at nrcan-rncan.gc.ca> wrote:
Rohini, Try setting all the zone level outside air fields to the
smallest number you can enter.
Kamel Haddad
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of R B
Sent: April 19, 2011 10:21
To: eQUEST Users List
Subject: [Equest-users] OA hourly data
Hello all:
I am trying to simulate zero outside air. I set the min OA on
the systems tab to zero, economizer to fixed fraction, there are no OA
numbers at the zone level. I would assume this will give me zero OA but
when I look at the hourly variables (ratio of outside air to supply flow
- Var 39, and the minimum OA damper position - Var 80) they vary from
0.21 to 0.56.
What am I missing? Any pointers helpful.
-Rohini
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/312861c5/attachment-0002.htm>
More information about the Equest-users
mailing list