[Equest-users] Electric water heaters EF / EIR
    Bishop, Bill 
    wbishop at pathfinder-ea.com
       
    Wed Apr 20 17:25:48 PDT 2011
    
    
  
Mark,
I'd use HIR=1/EF and then zero out the tank losses by entering Tank
UA=0.
Regards,
Bill
 
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
 
 134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
wbishop at pathfinder-ea.com           www.pathfinder-ea.com
<http://www.pathfinder-ea.com/> 
P   Sustainability - the forest AND the trees. P    
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mark
Darrall
Sent: Wednesday, April 20, 2011 7:55 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Electric water heaters EF / EIR
 
I have a 6kw 40 gal electric DHW. The EF per 90.1 Table 7.8 is 0.87 (is
that right?). What should I input for the EIR? The inverse of the EF?
I'm better at moving air than electrons...
 
Thanks!
 
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
 
 
 
DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
 
A2SO4 Architecture, LLC
Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL  317 388 8850
FAX  317 280 0692
MOB 765 749 0841
www.a2so4.com
 
Please consider the environment before printing this e-mail.  
 
CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
confidential and intended solely for the use of the individual or entity
to which they are addressed. If you are not the intended recipient, you
may not review, copy or distribute this message. If you have received
this email in error, please notify the sender immediately and delete the
original message. Neither the sender nor the company for which he or she
works accepts any liability for any damage caused by any virus
transmitted by this email.
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110420/32864bb8/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110420/32864bb8/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2061 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110420/32864bb8/attachment-0005.jpeg>
    
    
More information about the Equest-users
mailing list