[Equest-users] Radiant ceilings
    Arpan Bakshi 
    arpanbakshi at gmail.com
       
    Mon Apr 25 10:54:36 PDT 2011
    
    
  
Shalini
An alternate method is using fan coil units with turned down fans. Have you
tried this already?
On Mon, Apr 25, 2011 at 1:34 PM, Rob Hudson <rdh4176 at gmail.com> wrote:
> eQuest forces the cooling system of "VAV" to chilled water.  if you use
> "PVAV" or packaged VAV, then the cooling type is forced to be DX coils.
>
> Happy Monday!
>
> Rob
>
> On Mon, Apr 25, 2011 at 1:31 PM, Shalini Modi <shalinimodi at msn.com> wrote:
>
>>  Hello all,
>>
>> I need to model radiant ceiling for heating and cooling both. As per the
>> suggestions in the archive (quoted below), I kept the system as VAV, reduced
>> fan usage to represent radiant slab system's fan usage, kept my heating by
>> water loop baseboards and cooling by DX and coil head and loop temperatures
>> as per radiant slab system but after selecting the system type as 'VAV', in
>> the cooling page, it won't allow me to select 'electric DX' as the cooling
>> source.
>>
>> Kindly advice how can I solve this problem.
>>
>> Thanks a lot,
>>
>> Shalini
>>
>> [Equest-users] How do I model a building with radiant slab heat ANDair
>> conditioning? *Bishop, Bill* wbishop at pathfinder-ea.com
>> <equest-users%40lists.onebuilding.org?Subject=Re%3A%20%5BEquest-users%5D%20How%20do%20I%20model%20a%20building%20with%20radiant%20slab%20heat%0A%09ANDair%20conditioning%3F&In-Reply-To=%3C83996EE70003D04B830E1C4A5E6688CEEFA58A%40PATHMAIL2.pathfinderengineers.com%3E>
>> *Tue Mar 2 14:03:52 PST 2010*
>>
>>    - Previous message: [Equest-users] How do I model a building with
>>    radiant slab heat AND air conditioning?
>>    <http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/003453.html>
>>    - Next message: [Equest-users] ASHRAE Baseline EUI
>>    <http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/003420.html>
>>    - *Messages sorted by:* [ date ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/date.html#3454> [
>>    thread ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/thread.html#3454> [
>>    subject ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/subject.html#3454> [
>>    author ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/author.html#3454>
>>
>> ------------------------------
>>
>> Rob,
>>
>> Select the system based on the DX air conditioning, then add hot water
>> baseboards for the radiant slab. Set your baseboard capacity, coil head,
>> loop temperature etc. to match the radiant slab heating system.
>>
>>
>> Regards,
>> Bill
>>
>> William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
>> Mechanical Engineer
>>
>> 134 South Fitzhugh Street
>> Rochester, NY 14608
>> T: (585) 325-6004 Ext. 114
>>
>> F: (585) 325-6005
>> wbishop at pathfinder-ea.com <http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
>> www.pathfinder-ea.com
>> P Please strive to live sustainably.
>> ________________________________
>>
>> From: equest-users-bounces at lists.onebuilding.org <http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
>>
>> [mailto:equest-users-bounces at lists.onebuilding.org <http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>] On Behalf Of Rob
>> Rosen
>> Sent: Tuesday, March 02, 2010 4:34 PM
>>
>> To: equest-users at lists.onebuilding.org <http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
>> Subject: [Equest-users] How do I model a building with radiant slab heat
>>
>> ANDair conditioning?
>>
>> To All,
>>
>> Is it possible to model a building with radiant slab heat (hot water
>> loop) and air conditioning? It appears to me that the eQUEST airside
>> system type for radiant slab heating is FPH (floor panel heating
>>
>> system), and that this is "heating only".
>>
>> Can anyone suggest a way to model a building that has both radiant slab
>> heating and DX air conditioning?
>>
>> Thanks,
>>
>> Rob Rosen
>> Senior Energy Analyst
>>
>> Taitem Engineering
>> 110 S. Albany St.
>> Ithaca, NY 14850
>> Phone: 607-277-1118 ext 110
>> Fax: 607-277-2119
>> www.taitem.com
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100302/e0ae9990/attachment.htm>
>>
>> ------------------------------
>>
>>    - Previous message: [Equest-users] How do I model a building with
>>    radiant slab heat AND air conditioning?
>>    <http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/003453.html>
>>    - Next message: [Equest-users] ASHRAE Baseline EUI
>>    <http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/003420.html>
>>    - *Messages sorted by:* [ date ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/date.html#3454> [
>>    thread ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/thread.html#3454> [
>>    subject ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/subject.html#3454> [
>>    author ]<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-March/author.html#3454>
>>
>> ------------------------------
>> More information about the Equest-users mailing list<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
> --
> Rob Hudson
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-- 
*
*
*
Arpan Bakshi  LEED AP BD+C
*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110425/12b13212/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list