[Equest-users] equest and energy plus outputs
    Joe Huang 
    yjhuang at whiteboxtechnologies.com
       
    Fri Apr 29 01:56:17 PDT 2011
    
    
  
Please note that the link for my paper should be 
http://www.whiteboxtechnologies.com/downloads/SimBuild2006_EPlusDOE2_translatorF.pdf,
not what was written below.  Sorry for the mistake.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
Joe Huang wrote:
> I did not think my previous reply to Deepika would engender so much 
> traffic on this topic, but after reading through the various posts
> I feel compelled to add further comments because I think there's been 
> some misunderstanding or misperceptions abou comparing results 
> between  two programs, in this case, specifically EnergyPlus and 
> eQUEST or DOE-2:
>
> 1) Several people (some even in private e-mail) have mentioned  
> looking at the BESTTEST or SP-140 test runs that are repeated 
> everytime there's a new EnergyPlus release. Those simulations are 
> extremely simplified test cases, mostly of one-zone models designed to 
> test fundamental heat transfer algorithms - the impact of solar gain, 
> wall heat loss, thermal mass - across various programs. These test cases
> do not begin to address the dynamic conditions found in any real 
> building, particularly not a large commercial building.  
> Unfortunately, it's
> these interactions between the transient loads and the HVAC system 
> response that will color or dominate the resultant energy numbers.
> In my opinion, a far more revealing test suite would be either the CEC 
> Title 24 certification test suite or even the ten DOE-2 sample runs,
> where the models are of realistic buildings with typical systems and 
> operating controls (for more details on the Title-24 certification 
> test suite, please see my  SimBuild 2006 paper, available for download 
> at http://www.wbt/downloads/SimBuild2006_EPlusDOE2_translatorF.pdf ).  
> My point is that the BESTTEST/SP140 results may show that the basic 
> heat transfer algorithms in the programs are (reasonably) consistent, 
> but that doesn't mean the programs will show similar results when used 
> to model actual buildings, particularly not commercial buildings with 
> intermittent operations and complex HVAC systems and controls.
>
> 2) Several people sounded incredulous that the differences could be as 
> much as 50%.  I can only say that if you try it, i.e., model the same 
> building (preferably not a shoebox with a window on one side :-)) with 
> two programs, you will quickly appreciate the difficulty. Actually, 
> from my vantage point, 50% does not sound exaggerated at all. I just 
> got back from a simulation workshop in China, where differences of 
> several hundred percent were reported comparing programs such as 
> DOE-2.1E, TRNSYS, and DeST, a Chinese program, even though they were 
> looking only at residential apartment buildings. The dirty secret in 
> our field is that even if you asked two reasonably competent modelers 
> to model the same building with the same program, they're apt to come 
> up with quite different results. Doing it with two different programs 
> just makes that match exponentially more difficult.
>
> 3) Several people (including me) have alluded to the difficulty in 
> making the inputs consistent. I cannot emphasize this enough. All 
> programs have hundreds of hidden defaults or assumptions that aren't 
> necessarily transferable. My paper highlights nine of the most 
> prominent ones found in the CEC project, e.g., DOE-2 models drapes as 
> a SHADING-FRACTION, EnergyPlus models them as internal shading surface 
> requiring 10 inputs; DOE-2 allows a distribution loss in the water 
> loop, EnergyPlus didn't; DOE-2 degrades the wind speed in its 
> infiltration calculation, EnergyPlus didn't; DOE-2 allows a thermostat 
> throttling range; EnergyPlus didn't; etc., etc. (some of these 
> limitations in EnergyPlus may have been corrected since 2007).   Since 
> I had access to both the DOE-2 and EnergyPlus source code at the time, 
> I believe I did the most thorough job possible in matching inputs, but 
> even so I had to "punt" in numerous places (no drapes, infiltration at 
> raw wind speed, etc.) for the sake of an "apples-to-apples" 
> comparison.  Yet, even under these ground rules, I was still seeing up 
> to 40% differences in heating loads in some cases.
>
> 4) So which are the correct, or better, results?  I really can't say. 
> When you look into the codes, there is room for questioning the 
> solution techniques in both programs. Just by dint of having seen many 
> more DOE-2 results, I tended to regard them as the "conventional 
> wisdom", but then conventional wisdom could always be wrong. Maybe we 
> have been overestimating the heating energies in California all these 
> years. After reading through this litany of problems, some may want to 
> throw up their hands and say either, "it's hopeless" or even, "who 
> cares?". That to me is a wrong and dangerous response, because it 
> ultimately damages the credibility of simulations. Going back to 
> China, many experts there have become disenchanted and distrustful of 
> simulations,  and are calling for it NOT to be used for compliance 
> calculations. The same can happen here, as well. So, I think we need 
> to spend more effort to have a better sense of the relative 
> performance of different programs, and what is the "ground truth". 
> Doing a parallel set of calibrated simulations against good monitored 
> data would be a good start. 
>
> Joe
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 108D
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com
> www.whiteboxtechnologies.com
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>   
>
>
> Paul Diglio wrote:
>> Mizra:
>>
>> Thank you for the time it took you to send the results of your study 
>> to the forum.  Some of the top simulation firms in my area use Energy 
>> Plus and I was confused when other people claimed a higher 
>> discrepancy rate than you modeled.
>>
>> Paul Diglio
>>
>> *From:* Mirza Sajjal <Mirza.Sajjal at BuroHappold.com>
>> *To:* Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com>; deepika 
>> khowal <deepika.khowal at gmail.com>
>> *Cc:* equest-users at lists.onebuilding.org; energyplus_support 
>> <EnergyPlus_Support at yahoogroups.com>
>> *Sent:* Thu, April 28, 2011 5:55:09 PM
>> *Subject:* Re: [Equest-users] equest and energy plus outputs
>>
>> This was a little study I did out of curiosity last year, and the 
>> results between eQUEST (v3.63) and EnergyPlus (v4.0) matched quite 
>> well (~1.4% difference). All the schedules, zone areas, surface areas 
>> were exactly the same (I checked), but I also chose a simple system; 
>> PTAC units for the comparison. I believe when I was doing this I had 
>> checked the performance curves that were being used in EnergyPlus and 
>> they matched the eQUEST curves.
>>
>>  
>>
>> I assume the results will begin to differ when the systems become 
>> more complicated, but even then I believe if both models are 
>> calibrated to match as much as possible the results shouldn’t vary 
>> significantly (assuming all systems are native to the programs and 
>> we’re not creating work-arounds i.e. DOAS in eQUEST using dummy zones 
>> or the like).
>>
>>  
>>
>> (FYI, the geometry was ported over to EnergyPlus through a tool I 
>> wrote using Excel and VBA, but it’s a messy process)
>>
>>  
>>
>> Following are some of the results and graphical outputs:
>>
>>  
>>
>>  
>>
>>  
>>
>>  
>>
>>  
>>
>>  
>>
>>  
>>
>>  
>>
>>  
>>
>> *____________________***
>>
>> *Mirza Sajjal*
>> Engineer
>>
>>  
>>
>> Buro Happold
>> 100 Broadway
>> New York, NY 10005
>>
>> Tel: +1 212 334 2025
>>
>> Direct: +1 212 616 0380
>>
>>  
>>
>> *From:* equest-users-bounces at lists.onebuilding.org 
>> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
>> *Pasha Korber-Gonzalez
>> *Sent:* Thursday, April 28, 2011 4:46 PM
>> *To:* deepika khowal
>> *Cc:* equest-users at lists.onebuilding.org; energyplus_support
>> *Subject:* Re: [Equest-users] equest and energy plus outputs
>>
>>  
>>
>> As I understand it--Energy+ is free-ware in it's raw form.    I guess 
>> I was wrong to make an assumption that Deepika is using it without an 
>> interface.    If this is not the case it might explain such a 
>> variance in results.     When I model in DOE-2 raw form---it is so 
>> much harder for me to manage my data and inputs in my head and 
>> such----I was not born to be a programmer, and it gives me nightmares 
>> from struggling to pass FORTRAN so many years ago...ugh.
>>
>>  
>>
>> Therefore, I haven't looked at E+ myself for a very long time and 
>> purchasing or putting out the cost for the user-interface programs is 
>> not as desireable as using the eQuest free-ware.  or the future 
>> CANQuest free-ware (future SI version).
>>
>>  
>>
>> BUT-- I know that E+ is supposed to have some great capabilities in 
>> which we are limited with DOE-2 (to an extent.)    Has anyone else 
>> had the time and desire to compare these program engines more closely 
>> recently?   Also--why is it so difficult to "match" systems in eQuest 
>> and E+....forgive my blase'-ness, but isn't a pkgd system a pkgd 
>> system...a pkgd system???  :)
>>
>> Pasha
>>
>>
>>  
>>
>> On Thu, Apr 28, 2011 at 11:39 AM, deepika khowal 
>> <deepika.khowal at gmail.com <mailto:deepika.khowal at gmail.com>> wrote:
>>
>> So based on my analysis, there is a difference of about 10% in 
>> results of equest and E+. I would believe that because there are 
>> certain parameters which are very difficult to match.
>>
>> this seems reasonable to me.
>>
>>  
>>
>> On Thu, Apr 28, 2011 at 9:09 AM, John Aulbach <jra_sac at yahoo.com 
>> <mailto:jra_sac at yahoo.com>> wrote:
>>
>> I am sure EnergyPlus is a fine and well thought out program (consider 
>> the sources and fine people involved).  However, since I am in 
>> production mode (and don't have time to create a model in two 
>> different programs-who pays for THAT), I chose to migrate to eQuest 
>> after DOE-2.1 A, B, C, D, and E. There are plenty of resources to ask 
>> questions of, the program started out in Windows (didn't need "add 
>> ons"), and gives me a 3-D rendering on the building immediately.
>>
>>  
>>
>> I dealt with 20 years of "raw" DOE-2, where I didn't know what my 
>> building really looked like (until Joe Huang came along with BDL 
>> Draw..). So I would need at age (you guess..) to not relearn an 
>> entirely new program and stick with what I had learned over the past 
>> 25+ years.
>>
>>  
>>
>> John R. Aulbach, PE, CEM
>>
>> Senior Energy Engineer
>>
>> *Partner** **Energy*
>>
>> 1990 E. Grand Avenue, El Segundo, CA 90245
>> W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
>>
>> www.ptrenergy.com <http://www.ptrenergy.com/> | 
>> jaulbach at ptrenergy.com <mailto:%7C%20jaulbach at ptrenergy.com>
>>
>>  
>>
>>
>>  
>>
>>  
>>
>> *From:* deepika khowal <deepika.khowal at gmail.com 
>> <mailto:deepika.khowal at gmail.com>>
>> *To:* Paul Diglio <paul.diglio at sbcglobal.net 
>> <mailto:paul.diglio at sbcglobal.net>>
>> *Cc:* equest-users at lists.onebuilding.org 
>> <mailto:equest-users at lists.onebuilding.org>; energyplus_support 
>> <EnergyPlus_Support at yahoogroups.com 
>> <mailto:EnergyPlus_Support at yahoogroups.com>>
>> *Sent:* Thu, April 28, 2011 8:56:34 AM
>>
>>
>> *Subject:* Re: [Equest-users] equest and energy plus outputs
>>
>>
>> As Joe and others mentioned, its really difficult to create all 
>> parameters same in both softwares.
>>
>> I am still working on it .
>>
>> For ex, which system should I use in equest as equivalent to unitary 
>> system in E+?
>>
>> I understand its difficult to match every input and hence, getting 
>> same results is very tricky.
>>
>> Thanks all for their inputs
>>
>>  
>>
>> On Thu, Apr 28, 2011 at 4:54 AM, Paul Diglio 
>> <paul.diglio at sbcglobal.net <mailto:paul.diglio at sbcglobal.net>> wrote:
>>
>> I thought E+ is a free program?  I would be interested to hear from 
>> anyone who has used Google SketchUp and the Open Studio Plug-in to 
>> generate a 3D view in E+.
>>
>> I would like to hear more about the discrepancies between eQuest and 
>> E+ from those who use both programs.
>>
>> Paul Diglio
>>
>>  
>>
>>  
>>
>> *From:* Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com 
>> <mailto:pasha.pkconsulting at gmail.com>>
>> *To:* deepika khowal <deepika.khowal at gmail.com 
>> <mailto:deepika.khowal at gmail.com>>
>> *Cc:* energyplus_support <EnergyPlus_Support at yahoogroups.com 
>> <mailto:EnergyPlus_Support at yahoogroups.com>>; 
>> equest-users at lists.onebuilding.org 
>> <mailto:equest-users at lists.onebuilding.org>
>> *Sent:* Thu, April 28, 2011 1:27:44 AM
>> *Subject:* Re: [Equest-users] equest and energy plus outputs
>>
>>  
>>
>> Hmmm- an energy plus model showed 50% less energy use (EUI) than 
>> eQuest?   Did you use the same weather files?  (i.e. convert the EPW 
>> you used in E+ to .bin and use the same weather file in eQuest?)
>>
>>  
>>
>> If this is truly the case, this is unsettling as a simulator.   
>> Wouldn't it be safer for our clients to error on the conservative 
>> side and give the eQuest results instead of the E+ results?
>>
>>  
>>
>> Also--if this is the case, then what is the market advantage to 
>> spending thousands of dollars on E+ software rather than use the 
>> FREE-ware eQuest program??
>>
>>  
>>
>> I'd appreciate any commentary to help me "see the light" of this 
>> topic.  And if Deepika is willing to share a visual of his energy 
>> results output, I'm super curious to see what it is showing...
>>
>>  
>>
>> Good question/good info...thanks,
>>
>> Pasha
>>
>>  
>>
>> Korber Energy Consultants
>>
>>
>>
>>  
>>
>> On Wed, Apr 27, 2011 at 7:11 PM, deepika khowal 
>> <deepika.khowal at gmail.com <mailto:deepika.khowal at gmail.com>> wrote:
>>
>> Thanks Joe
>>
>> Even I realized the same thing. the total energy use in Energy plus 
>> was almost 50% less than equest.
>>
>> If this is the case, who would you know that you model is working fine?
>>
>>  
>>
>> On Wed, Apr 27, 2011 at 6:06 PM, Joe Huang 
>> <yjhuang at whiteboxtechnologies.com 
>> <mailto:yjhuang at whiteboxtechnologies.com>> wrote:
>>
>> I was involved in a two year project 2005-2007 to convert the Calif. 
>> Energy Commission's Title-24 certification suite of building tests 
>> from DOE-2.1E to EnergyPlus.  There are some areas where it's 
>> difficult to get comparable inputs due to differences or limitations 
>> in the models. The differences between the two programs varied a lot 
>> depending on the building, weather, and HVAC system. For the CEC 
>> certification suite of 160 runs, cooling results were more 
>> consistent, within 10% in most cases, with EnergyPlus almost always 
>> on the high side; for heating, the differences were much greater, 
>> sometimes with EnergyPlus being 40-60% lower than DOE-2.1E.  I have a 
>> 120-page report on this comparison, but haven't bothered to put it on 
>> the Web.
>>
>> Joe
>>
>> Joe Huang
>> White Box Technologies, Inc.
>> 346 Rheem Blvd., Suite 108D
>> Moraga CA 94556
>> yjhuang at whiteboxtechnologies.com 
>> <mailto:yjhuang at whiteboxtechnologies.com>
>> www.whiteboxtechnologies.com <http://www.whiteboxtechnologies.com/>
>> (o) (925)388-0265
>> (c) (510)928-2683
>> "building energy simulations at your fingertips"
>>
>>
>>
>> deepika khowal wrote:
>>
>> HI All
>> I am trying to create same model in equest and energy plus to see 
>> whether i see same results and just to validate my simulation files.
>> has anyone done this before?
>> I would like to know what is the % difference in both software outputs?
>> Thanks
>> Deepika
>>
>> ------------------------------------------------------------------------
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to 
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
>> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>>  
>>
>>  
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to 
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
>> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>>
>>  
>>
>>  
>>
>>  
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to 
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
>> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>>
>>  
>>
>> This message has been scanned by MailController - 
>> portal1.mailcontroller.co.uk <http://portal1.mailcontroller.co.uk> |
>>
>> This message has been scanned by MailController 
>> <http://portal1.mailcontroller.co.uk/>.
>>
>>  
>>
>> This message has been scanned by MailController - 
>> portal1.mailcontroller.co.uk |
>>
>> This message has been scanned by MailController 
>> <http://portal1.mailcontroller.co.uk/>.
>>
>>  
>>
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 52713 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0018.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22695 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0019.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 12136 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0020.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 10595 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0021.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 10289 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0022.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 18621 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0023.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 33966 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0024.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 53001 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0025.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 75984 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110429/c60a4ddb/attachment-0026.jpeg>
    
    
More information about the Equest-users
mailing list