Hi Brad!
You can't have one without the other. eQuest uses both the schedules
and a W/SF figure for each space in tandem. The schedules provide an
hourly fraction of the defined W/SF, not W/SF values directly. If you
aren't explicitly defining a unique lighting schedule, it only means
eQuest is creating one for you based on your other inputs in the wizards
(weighted space type allocations alongside the W/SF entered or defaulted
for each space type). You can observe the net result after closing the
wizards by double clicking on the schedule in the component tree.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bradley
Donohue
Sent: Wednesday, August 10, 2011 10:00 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Lighting Schedules
Hello,
I am fairly new to equest and have a quick question about lighting
schedules. If the lighting schedules are left as undefined but there is
a w/ft2 value entered will equest include the w/ft2 value in any way?
Thanks,
Brad