[Equest-users] evaporative coolers in equest
deepika khowal
deepika.khowal at gmail.com
Tue Aug 16 13:11:15 PDT 2011
This is an existing building with evaporative coolers.
the proposed design to upgrade the windows and check the relative benefits.
I dont see much benefits in energy because evaporative coolers are sized
based on Cfm and not btus, the savings will be in cfms.
correct me if I am wrong.
is there any other way I can show the benefit in the proposed case if not
HVAC benefits?
Thanks
On Tue, Aug 16, 2011 at 1:00 PM, Nick Caton <ncaton at smithboucher.com> wrote:
> Hi Deepika,****
>
> ** **
>
> I’m not certain any increase/decrease in cooling loads (such as solar loads
> affected by changing glazing) should have any effect on the reported “space
> cooling energy” when you’re using evaporative coolers. Direct evaporative
> (swamp) coolers of the simplest sort have only fan and pump energies to
> consider - no refrigerant! I would advise looking up the Detailed
> Simulation Reports Summary page 158/160 to review end use categories and
> what they cover. ****
>
> ** **
>
> I am unfamiliar with Bridgeport’s climate, but as a general rule if I
> observed a significant amount of glazing in a space served by a direct
> evaporative cooler… I’d be extra cautious to ensure the HVAC designer is
> carefully considering condensation and potential for other humidity-driven
> issues along the way. I’m most used to seeing them applied to
> well-ventilated and/or open-air spaces such as garages and gyms/hangars.**
> **
>
> ** **
>
> ~Nick****
>
> ** **
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER****
>
> ** **
>
> Smith & Boucher Engineers****
>
> 25501 west valley parkway, suite 200****
>
> olathe, ks 66061****
>
> direct 913.344.0036****
>
> fax 913.345.0617****
>
> www.smithboucher.com* *****
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *deepika khowal
> *Sent:* Tuesday, August 16, 2011 1:36 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] evaporative coolers in equest****
>
> ** **
>
> Hello all****
>
> I am modeling a building in Bridgeport, CA which has evaporative coolers.*
> ***
>
> I dont see any benefits if I replace existing clear glass with low-e in
> cooling energy consumption.****
>
> Did anyone model evaporative coolers/swamp coolers before?****
>
> I want to know whether there is a way to show cooling benefit with such
> HVAC system.****
>
> Thanks****
>
> Regards****
>
> Deepika****
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110816/2d4431e7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110816/2d4431e7/attachment-0002.jpeg>
More information about the Equest-users
mailing list