[Equest-users] Underheating warning for bunch of zones
Demba Ndiaye
Demba.Ndiaye at setty.com
Thu Dec 1 05:46:44 PST 2011
Niko,
The basic problem in your model is that you do not call the hot water loop or the furnace. For the main coil to get active, you have to input a temperature setpoint (HEAT-SET-T) - see enclosed illustration (the values shown in the enclosed are for illustration purpose: adapt to your case). And for the reheat to come on, you have to also input a setpoint (see again enclosed illustration).
There are some other input problems we can discuss off-list.
[cid:image006.jpg at 01CCB005.C0AD9C30]Demba Ndiaye, Ph.D., P.E., LEED AP BD+C, BEMP
Energy Analyst/Mechanical Engineer
Setty & Associates, Ltd.
MEP Design Engineering | Project Management
|Construction Management | Design-Build Services | Commissioning
|3040 Williams Drive, Suite 600 | Fairfax, VA 22031
|Voice 703.691.2115 | Fax 703.691.8084 | cell 571.830.9913
demba.ndiaye at setty.com<mailto:demba.ndiaye at setty.com> | www.setty.com<http://www.setty.com/>
This e-mail and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. If you are NOT the intended recipient or the person responsible for delivering the e-mail to the intended recipient, be advised that you have received this e-mail in error and that any use, dissemination, forwarding, printing or copying this e-mail is strictly prohibited.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nikola Kravik
Sent: Wednesday, November 30, 2011 6:00 PM
To: Rob Hudson
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Underheating warning for bunch of zones
Rob/all,
I don't have baseboards, it's basic VAV/w reheat system-I was trying to use the baseboards just to see if the zone heating kicks in.
I've attached the zip file, it's giving me the same warning that the zones are under heated and also 1 error that the "hot water loop has zero design flow".
I'm stuck and not sure how to go about it. Please point/help me understand how to go about the error fix....
I appreciate your feedback.
Best,
Nikola
From: Rob Hudson [mailto:rdh4176 at gmail.com]
Sent: Tuesday, November 29, 2011 12:03 PM
To: Nikola Kravik
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Underheating warning for bunch of zones
I would first check your system level inputs. Have you used a VAV system? if so, you need to know that these systems don't like to use the heating coil in the air handler and therefore you need to specify a reheat coil size and a preheat coil. Also, if you have baseboards in the model, they don't like to operate very well when set to activate to outdoor conditions. I always set the baseboard control to thermostat.
Hopefully these few tips help out.
Rob
On Tue, Nov 29, 2011 at 2:52 PM, Nikola Kravik <NKravik at willdan.com<mailto:NKravik at willdan.com>> wrote:
hi,
I'm simulating CHW Plant with CAV AHU's and bunch of packaged/split system units around supporting areas of the hospital/clinic.
I get the warning messages similar to below for almost all my zones and my gas heating hot water is extremely low, no matter what I try do on the heating side. I added baseboards but it didn't make a difference-still have bunch of zones underheated looking at the ss-o's.
Do you any other hints you can share where else to look for the HHW low consumption?
Best,
Nikola
[cid:image001.png at 01CCB005.0E6D7040]
[cid:image002.jpg at 01CCB005.0E6D7040]
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/6b10ae1a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 47313 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/6b10ae1a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 92188 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/6b10ae1a/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 167 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/6b10ae1a/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 15865 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/6b10ae1a/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 2912 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/6b10ae1a/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Capture.JPG
Type: image/jpeg
Size: 93733 bytes
Desc: Capture.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/6b10ae1a/attachment.jpeg>
More information about the Equest-users
mailing list