[Equest-users] Chiller number and size of the ASHRAE 90.1
Rob Hudson
rdh4176 at gmail.com
Mon Dec 12 06:38:48 PST 2011
If it is only used to cool the process, and not cool the space that the
process is in (ie a data rack room that has a cooling system) then you
should use the as designed efficiency. You may want to separate the
pumping energy, if any, as well by creating a second chilled water loop.
If you are cooling a space that happens to have a high heat load due to
the functioning equipment, you may be able to take credit for an efficient
design. Its a dance that for LEED may need to be very carefully thought
out.
Hope this helps, and I hope others agree with me.
2011/12/12 Esmireta <e2fye2 at 163.com>
> Dear all,
> According to the Table G3.1.3.7 of the ASHRAE90.1, the number and type of
> chillers could be determined. But I encountered a project of a industry
> factory, in which the industry process need a lot of cooling. I notice the
> Table G3.1.3.7 is for "Building Peak Cooling Load", I take it as the
> industry cooling will not be included in the Building Peak Cooling Load, is
> it correct? If so, is there any efficiency, number or type requirement of
> the industry chiller? Can I exclude the industry cooling energy in the
> building energy simulation?
> Thanks!
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111212/50090aef/attachment-0002.htm>
More information about the Equest-users
mailing list